Hello from Dayton, Ohio.

I love this question!  The periodicity of ice ages is about 50,000 years.
The effects from glaciers is only periodic and not continuous.  In fact,
I am told that if you sit in one place, you can see Kudzu grow, but if your
period of observation is continuous, the growth of Kudzu is hazardous
to your well being.  The effect of the TNV is defined as being safe, similar
to SELV, since the ring voltage is intermittent, but I still would not like 
to
be shocked by the 120V ring voltage.  In this case the ring time is about
one second in length.  How long does the ring tone have to be to become
hazardous?   The GFCI will interrupt in about a 100th of a second and
again, I would not want to get shocked by a voltage to have the GFCI
to kick in.  I am confident that the energy in the GFCI circuit is very 
high,
so is this better than the clause 1.2.8.7 on Haz Energy.    If the GFCI
operated in one tenth of a second would this be hazardous?

There is a popular book with the title some what like coming into the light, 

where the author was struck by a continuous bolt of lightning and lived to 
tell
all.  There is a veiled relationship between the hazard severity and the 
length
of the time for exposure.  How short is short for being intermittent and how 
long
is long for being continuous.  The threshold of acceptability for the pain 
or
physical reaction, blister, etc, and the rate of delivery of the energy to 
the
person, hand, skin, etc. determines what is short and just too long.

A similar pet peeve of mine is the frequency of occurrence versus the
severity of the event or hazard.  One pundit proposes that there is a
zone of acceptability between the graph of these two, but I believe that
hazard reduction is for safety and frequency reduction is the domain of
insurance statisticians.

So can we develop a graphical representation of the length of time of
exposure versus the severity of the hazard and have a zone of safety?
The continuous level is not an asymptote but a parallel to one axis of
the coordinate system.   So any point under the parallel must be safe.

So I would ask Rich's question the other way around, when can we stop
the test for a continuous application of a hazard?  One hour; 2 weeks, etc.?

To answer Rich's question, any point of time under the parallel is part of
of the continuum, including ground zero, at the inception of the application
of the hazard.

Manning Rose
NCR Corporation
[email protected]
 ----------
>From: Rich Nute
>To: emc-pstc
>Subject: How long for continuous?
>Date: Tuesday, November 12, 1996 4:46PM
>
>Hello from San Diego:
>
>With regard to IEC 950:
>...........................................................
>1.2.8.7   HAZARDOUS ENERGY LEVEL:  A stored energy level of
>20 J or more, or an available continuous power level of 240
>VA or more, at a potential of 2 V or more.
>...........................................................
>At what point in time after start of the measurement is the
>available power considered "continuous"?
>
>In the application, a fuse is used to limit the continuous
>power to less than 240 VA.  At 240 VA, the fuse WILL operate --
>but it may take up to the maximum fuse operating time.
>
>Is this okay?
>
>If not, what is the time after which 240 VA is considered to
>be continuous?
>
>Best regards,
>Rich
>
>
>-------------------------------------------------------------
> Richard Nute                             Quality Department
> Hewlett-Packard Company           Product Regulations Group
> San Diego Division (SDD)          Tel   :      619 655 3329
> 16399 West Bernardo Drive         FAX   :      619 655 4979
> San Diego, California 92127       e-mail:  [email protected]
>-------------------------------------------------------------
>
>
>
>
>

Reply via email to