Simply, no.  There are special tests performed to determine if a cable is made 
from low smoke producing, slow burning insulating materials.  The UL Standard 
is UL 910.  The type of Listed (not Recognized Component) cables that are 
appropriate for use in plenums have the cable designation followed by a "P" 
suffix.  For example, Type CM becomes Type CMP, Type CL2 becomes CL2P, etc.

BTW, a cable that has a VW-1 rating is typically Recognized Component Appliance 
Wiring Material (AWM), and may or may not be suitable for wiring external to 
equipment.  It is also worth noting that there are many cables that are both 
Recognized AWM for certain applications and are Listed for others (including 
general wiring applications [TH, TEW, etc.] and as machine tool wire [MTW], 
among others).

If your using AWM, double check to be certain that the cable is suitable for 
external use.  A 30 mil PVC jacket is a good starting point.  Check with the 
vendor and UL to see if the cable you're using is appropriate.

Putting cable into any environmental air space can bring on many additional 
restrictions.  Please refer to US NEC (NFPA70), Article 300-22 for additional 
details.  For installations in nonUS locations, check the local  installation 
electrical codes for applicable requirements.

Peter L. Tarver
Northern Telecom
[email protected]
------------------------------
     Hello everyone,

     We are using a cable with one of our product which is UL
     approved and passes UL VW-1 vertical flame test for rated temp.
     of 80C and rated voltage of 30V.

     Jacket material is PVC.

     We are wondering if a customer wants to route this cable through
     an air plenum of a building, is above approval sufficient? or
     there are some other OSHA standard which we need to meet?

     Any suggestions or comments is appreciated.

     [email protected]