Bob, 

A long time ago, before EDP (now ITE) equipment, the ground rules for maximum 
voltage of Class 2 circuits were defined at UL as 30 V rms, based on the Class 
2 limits defined in the National Electrical Code at that time (This was before 
NEC Class 3 circuits). So that definition took care of  bell ringing 
transformers which could be wired in your home without the conductors on the 
secondary  being run in conduit. 

When transistors came along they begat EDP equipment and the definition had to 
be enlarged to include 42.4 volts peak, to take care of the signals which are 
not sinusoidal on I/O ports (42.4 being 30 times the square root of 2, a 
reasonable method of getting to 42.4.). 

The step to 60 V DC came along when the NEC expanded Art. 725 to include Class 
3 circuits. I was never clear on the reason for Class 3 circuits, but I suspect 
that someone else on this net will educate us both soon. 

As far as the policy of working on energized equipment in your company is 
concerned, in my opinion the only safe circuit is a Class 2 circuit, or one 
that is dead and to which I have the only key to the circuit breaker 
controlling that circuit in my pocket. All other circuits are hazardous, and 
extreme caution must be taken if the person must work on it live, including a 
person standing by to render help if needed. I still remember showing up at 
Zinsco on a Monday morning to run tests on one of their big transformers only 
to find out that their chief engineer electrocuted himself on Saturday while 
getting the transformer ready. He was working on a live circuit, alone. 

Regards, 

Gabriel Roy
Hughes Network Systems
MD
The opinions expressed are mine and not those of HNS. 

P.S.         ".... electrical safe work practices policy (working on energized 
equipment)..." isn't that an oxi-moron? 


----------------------------------- 
snip-----------------------------------------------
>Hello again,


>I had previously asked for references to an alleged occupational requirement 
for a maximum touchable voltage of 24V and I thank you for your responses.
I saw nothing concrete which gave legitimacy for a 24V limit. I found the 
references to the telephone company interesting. I have another somewhat 
related question. What is the reasoning for selecting 42.2V peak and 60Vdc 
as a limit? Does UL explain this anywhere?

>The reason for this line of questioning is that I am involved in a debate on
an electrical safe work practices policy(working on energized equipment). The 
issue of applicability involves who is covered. Ideally everything should be 
de-energized before performing work, but that is not always the case. There 
are plenty of situations where that will not occur. So, the question is at 
what voltage should the policy kick in. 

>Regards,

>Bob Brister
Digital Equipment Corp.


 
 