Well, heck, why didn't you say so in the first place?

If you are talking about a workplace practice with a possible exposure, you
go to OSHA, not UL, ANSI, etc. 

29CFR 1910.303(g)(2)(i)"....live parts of electric equipment operating at 50
volts or more shall be guarded....."  Note that it does not distinguish
AC/DC.

29CFR1910.333(a)(1) "....Live parts to which an employee may be exposed shall
be deenergized before the employee works on or near them, unless the employer
can demonstrate that deenergizing introduces additional or increased hazards
or is infeasible due to equipment design or operational limitations. Live
parts that operate at less than 50 volts  to ground need not be deenergized
if there will be no increased exposure to electric burns or explosions due to
electrical arcs.

Keith Gershon
[email protected]
Electrical Safety Engineer

--------------------------------------
List-Post: [email protected]
Date: 7/12/96 10:10 AM
To: Keith Gershon
From: Bob
Received: by ehssmtp.lbl.gov with SMTP;12 Jul 1996 10:09:27 +0100
Received: from lbl.gov (lbl.gov [128.3.254.23]) by ehssun.lbl.gov (8.6.12/G)
with SMTP id KAA06566 for <[email protected]>; Fri, 12 Jul 1996
10:09:58 -0700
Received: from ruebert.ieee.org by lbl.gov (4.1/1.39)
        id AA22514; Fri, 12 Jul 96 10:09:53 PDT
Received: (from daemon@localhost) by ruebert.ieee.org (8.7.5/8.7.3) id
LAA14535 for emc-pstc-list; Fri, 12 Jul 1996 11:20:12 -0400 (EDT)
Message-Id: <[email protected]>
List-Post: [email protected]
Date: Fri, 12 Jul 96 11:01:47 EDT
From: Bob <[email protected]>
To: [email protected]
Cc: [email protected]
Apparently-To: [email protected]
Subject: RE: Why 42.4AC\ 60VDC
Sender: [email protected]
Precedence: bulk
Reply-To: Bob <[email protected]>
X-Resent-To: Multiple Recipients <[email protected]>
X-Listname: emc-pstc
X-List-Description: Product Safety Tech. Committee, EMC Society
X-Info: Help requests to  [email protected]
X-Info: [Un]Subscribe requests to  [email protected]
X-Moderator-Address: [email protected]



Hello again,


I had previously asked for references to an alleged occupational requirement 
for a maximum touchable voltage of 24V and I thank you for your responses.
I saw nothing concrete which gave legitimacy for a 24V limit. I found the 
references to the telephone company interesting. I have another somewhat 
related question. What is the reasoning for selecting 42.2V peak and 60Vdc 
as a limit? Does UL explain this anywhere?

The reason for this line of questioning is that I am involved in a debate on
an electrical safe work practices policy(working on energized equipment). The

issue of applicability involves who is covered. Ideally everything should be 
de-energized before performing work, but that is not always the case. There 
are plenty of situations where that will not occur. So, the question is at 
what voltage should the policy kick in. 

Regards,

Bob Brister
Digital Equipment Corp.


 