I do not have a copy of this standard, so I cannot speak directly to it, but
in general, when one is concerned with whether or not a 3ph load is balanced
or not, it is for one of 2 reasons:

1. Load calculation- If your total power is expessed in kW or kVA, then when
you translate this into amps for the purpose of fuse size, the overcurrent
protecter size will increase as the imbalance increases. Consequently the
conductor size will increase. Example, you have a 120/208Y 3 phase machine
rated at 36kW. If the load is perfectly balanced, the demand will be 100 amps
on each leg. But if the load is out of balance, the three legs could look
something like, 75-100-125 . You would have to fuse for the highest leg.

2. Neutral conductor size. The neutral conductor size is a function of the
greatest possible imbalance between any 2 legs.

--------------------------------------
List-Post: [email protected]
Date: 6/14/96 2:49 PM
To: Keith Gershon
From: Max
Received: by ehssmtp.lbl.gov with SMTP;14 Jun 1996 14:49:13 +0100
Received: from lbl.gov (lbl.gov [128.3.254.23]) by ehssun.lbl.gov (8.6.12/G)
with SMTP id OAA25477 for <[email protected]>; Fri, 14 Jun 1996
14:49:41 -0700
Received: from mail.ieee.org (rab.ieee.org) by lbl.gov (4.1/1.39)
        id AA17117; Fri, 14 Jun 96 14:49:05 PDT
Received: by mail.ieee.org (8.7.3/8.7.3)
        id OAA11227 for emc-pstc-list; Fri, 14 Jun 1996 14:16:56 -0400 (EDT)
Message-Id: <[email protected]>
To: [email protected]
Subject: "Balanced Three-Phase Equipment"
List-Post: [email protected]
Date: Fri, 14 Jun 1996 12:16:06 -0600
From: Max <[email protected]>
Sender: [email protected]
Precedence: bulk
Reply-To: Max <[email protected]>
X-Resent-To: Multiple Recipients <[email protected]>
X-Listname: emc-pstc
X-List-Description: Product Safety Tech. Committee, EMC Society
X-Info: Help requests to  [email protected]
X-Info: [Un]Subscribe requests to  [email protected]
X-Moderator-Address: [email protected]


I have an old, draft copy of IEC 1000-3-2.  In the definitions
section (section 3.14), it states the following:

        3.14....Balanced three-phase equipment
        Equipment having rated line currents which 
        differ by no more than 20%.

Then in section 4, it classifies equipment in two 4 classes and
under Class A, it says:

        Balanced three-phase equipment and all other
        equipment except that stated in one of the
        following classes:

So, what this seems to be saying is that both "balanced" and
unbalanced equipment falls under class A (if the equipment has an
input power greater than 600W.  

I'm not really very familar with safety regulations, but this
doesn't seem to make any sense to me.  What is the significance of
balanced three-phase equipment?  What are the issues involved if
the equipment presents an unbalanced load?  Are there any
requirements in Europe that require current balancing?

Thanks, Max