Vic Boersma invokes the definition of rated power in  IEC 950 to provide an
interpretation 
of the phrase in the LVD 'designed for use with a voltage rating of '. The
definition in IEC950 
is for the purposes of that directive and does not apply to the LVD. The LVD
itself does not 
give any further amplification of this point. What it does not say is 'powered
by a voltage with
a rating of'.  I know of no authoritive ruling on whether internally generated
voltages over 
the stated limit bring equipment within the scope of the directive. There is
none in the UK implimentation of the LVD, SI 1994 No. 3260 which uses a similar
phrase 'designed or adapted for use with a voltage rating' with no futher
amplification. I have always taken the
view that internally generated volages do bring equipment within the scope of
the directive but
I would be glad of information from anybody who knows of an authoritive ruling
on this
matter. 
If my assumption is right then the inaccessibility of the high voltages and the
high impedance 
of them will not remove the equipment from the scope of the directive or the
need to have
CE marking for this directive from next year. It will however make it easier to
meet the 
directive.
Nick Rouse. 

Reply via email to