I am wrestling with the concept of clearances as they apply
to our -50Vdc power circuits in a telecom application.
Looking at UL 1950 (3rd edition), Clause 3.4.1 says that
the
"connections" to a centralized dc power system are subject
to the requirements for primary circuits in accordance with
Cl 3.2. This is the
clause that relates to the power cordage, terminals, strain
relief, bushings, and such physical stuff.   OK, no
problem. Annex NAB offers no useful guidence for this at
all.

Clause 3.4.1 says nothing about treating the centralized dc
power CIRCUIT  as a PRIMARY CIRCUIT for clearance
considerations. More specifically, the NOTE under 3.4.1
defines the dc powered system as a SECONDARY circuit. I am
wondering if we should be using Table 3 for clearances at
all. What is the right interpretation about -50Vdc power
with
respect to creepage and clearance?

Is -50Vdc power SELV maybe?
And earthed as well because the plus return connects to a
master ground bar or equivalent.

I am also wondering if a power disconnect device [Clause
2.6] is
required  in a centralized dc power circuit. I see no
reference for this. This is sticky because, as you know,
switches or breakers to handle 50 Vdc at 10 amps are quite
large.  There are upstream feeder fuses, but fuses are not
on the
short list of approved disconnect devices in clause 2.6.2.
Can anyone please point me in the right direction?

Mike Donnelly
AG Communication Systems
Phoenix, AZ

 Mike Donnelly 

Reply via email to