Patrick, 

In response to your question:

>I didn't think GFI's used the ground lead. If
>there weren't any electrocutions from ground
>faults, it would not be related to the presence
>of a GFI.

>Having said that, I think a three-leaded version
>of a GFI could protect against line-neutral
>current imbalance, as well as high leakage
>current. Does anyone sell them?

According to the 1996 US NEC, 210-7 (a) all 15- and 20-ampere branch
circuit receptacles must be of the grounding type (this includes all GFCI
receptacles as required for kitchens, bathrooms, garages, etc.).  A
grounding type receptacle is one that has connections for a hot, neutral,
and ground.  Therefore, ALL standard GFCI receptacle's are what you call
"three-leaded versions".  Albeit, the GFCI circuitry is only connected to
the hot and neutral as described in previous messages on this topic. 

For replacement of old two blade (non-grounded) receptacles in
installations where there is no ground, 210-7 (d) of the NEC allows
replacement with 3-blade GFCI receptacles that are marked "No Equipment
Ground".  That means that cord connected  equipment designed with a chassis
ground for safety (IEC class 1) will actually have the chaises floated when
plugged into one of these receptacles.  This is not an oversight on the
part of the NEC writers but rather a vote of confidence in the additional
safety provided by GFCI's compared to older non-grounded receptacles.

Regards,

Mark Christopherson, P.E.
Irvine, California
email    [email protected]
Phone 714 251-2860
Fax      714 251-2868  