Hello from San Diego:


Several messages have suggested some values of current 
that cause ventricular fibrillation.  The values are all
over the map, and are much lower than those reported in
the research literature.  Here are some "better" facts
together with the source of those facts.

According to Biegelmeier and Lee, "New considerations
on the threshold of ventricular fibrillation for ac 
shocks at 50-60 Hz," IEE Proceedings, Part A, Vol. 127,
No. 2, March 1980, pp 103-110...

Research shows that the heart is not susceptible to 
fibrillation except during the T wave.  

The threshold of fibrillation for a heart exposed to 
an electrical current during a single T wave is 
relatively high, but for each consecutive T wave during 
which the current is present, the threshold decreases 
until it is about one-tenth of its initial value.  

For currents imposed hand-to-hand, the thresholds are 
believed to be above 500 mA if present during a single 
T wave, and above 50 mA if present during three or more 
consecutive T waves (heart-beats).

Furthermore, the shock current must exist for the full
duration of the T wave.

The T wave duration is about 15% of the heartbeat cycle.  
If we assume 60 beats per minute, then 15% of 1 beat
(1 second) is 150 milliseconds.

150 milliseconds is 7.5 cycles at 50 Hz, or 9 cycles 
at 60 Hz.

So, for fibrillation, the current would need to be at
least 500 mA for at least 7.5 cycles at 50 Hz or 9 cycles
at 60 Hz.

Or, the current would need to be at least 50 mA for at 
least 3 seconds.

GFCIs/RCCBs are designed to operate in 1 cycle/20 milli-
seconds or less at the rated current (GFCI = 5 mA, 
RCCB = 30 mA).  During that one cycle, the current can be 
up to 166 mA (assuming 250 volts and body impedance of 
1500 ohms).

So, GFCIs/RCCBs provide protection against fibrillation
by limiting the DURATION of the current applied to the 
body, given that the body impedance will cause a current
up to, say, 166 mA (250 V source) until the GFCI/RCCB trips.  
(At lower voltages, the current will be proportionately 
lower.)

Here are some ballpark numbers for 50-60 Hz currents:

    0.5 mA            Onset of sensation
    5   mA            Onset of tetanization ("can't let go")
   50   mA            Onset of fibrillation
  500   mA            Onset of cardiac, respiratory arrest
 5000   mA            Burns

Tetanization (freezing) only occurs with ac, and only then
in the frequency range of 20-100 Hertz.  Tetanization does
not occur with dc or with higher frequency ac.  

There is a famous experiment about the turn of the century
by D'Arsonval where he passed a current of 1 ampere through 
several humans, hand-to-hand, at 10 kHz, to light a light 
bulb!


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                             Quality Department 
 Hewlett-Packard Company           Product Regulations Group 
 San Diego Division (SDD)          Tel   :      619 655 3329 
 16399 West Bernardo Drive         FAX   :      619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------