Hello from San Diego:


IEC 742 (aka EN 60742) applies to transformers in general and
stand-alone transformers in particular.

IEC 742 contains some additional requirements for stand-alone
transformers compared to those in IEC 950 (aka EN 60950).

Unfortunately, IEC 1010 (aka EN 61010) does not contain specific
transformer requirements, so IEC 742 can be invoked if the test
house so chooses.

If your transformer is built-in, then I believe a transformer
complying with IEC 950 also complies with IEC 742.

It may be that the test house is simply saying that an IEC 950
certified transformer, by definition (not by test), does not 
comply with IEC 742.  In other words, they cannot accept, carte
blanche, the IEC 950 certification as being applicable to 
IEC 1010, whereas they could accept IEC 742 certification.

This may mean that the test house will need to conduct tests to
demonstrate compliance with IEC 1010.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                             Quality Department 
 Hewlett-Packard Company           Product Regulations Group 
 San Diego Division (SDD)          Tel   :      619 655 3329 
 16399 West Bernardo Drive         FAX   :      619 655 4979 
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------