From: John Garrett@HNS on 09/11/98 11:02 AM


To:   ieee pstc list <[email protected]>
cc:
Subject:  Inrush current and utility power line reistance

Hello All,

I have a question with respect to the typical  resistance of the mains
utility wiring; from the mains utility transformer into a residential or
industrial building.  But first a little history on the problem:

When testing a 30 W power supply at 120VAC, the inrush current at a phase
angle of 90 degrees measured 27A peak (4 unique sites were tested).
Calculating inrush current is a fairly straight forward application of ohms
law:

     Inrush Current = peak voltage divided by the dc resistance ( I = Vpeak
/ R)
(where R is the series resistance from the power line into the p/s through
the EMI  filter through the rectifier and the bulk capacitor back out the
other leg of the line)

In this application the result of the above equation is    I = (120
VAC*1.414) / 3.00 ohms  or  I = 56.6 Amps... where 3  ohms is the worst
case resistance internal to the power supply  (The assumption here being
there is little if any resistance external to the power supply that will
add significantly to this internal resistance).

 The problem is this: the calculated number (56.6 A) does not come close to
the measured (27A).  If fact, when we look at the measured data it appears
as if the external resistance, i.e. the resistance of residential or
industrial wiring from the utility mains transformer to the building and
internal to the building, is adding a very significant amount of resistance
(approx. 3.0 ohms).  This is very hard to believe!  But it is repeatable.
We are checking these measurements even as I write, but my questions are
simple.  First, am I missing something here with respect to second order
effects?  Second, does anyone have a feel for the resistance of the power
lines from the utility mains xfmr to the service entrance and into a
residential or industrial building?  Have any studies been performed that I
can refer to for this type of information?  Any help would be greatly
appreciated.




John Garrett                  Principal Engineer
Hughes Network Systems        Phone  (301) 601-2699
11717 Exploration Lane             FAX      (301) 428-2835
Germantown, MD 20876               Email: [email protected]



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], or [email protected] (the list
administrators).

Reply via email to