John,
 
 Let's see. hmmm.... 120Vac, 27A @ 90 degree phase angle (PA) and R approx 3 
 ohms. Actually it sounds as if you're mixing apples and oranges and getting 
 fruit cocktail.
 
 If I remember my basic circuits classes many, many years ago (clear those 
 cobwebs out), R always attributes to 0 degrees PA, therefore, I would have to 
 say that the 90 degrees PA you're expereincing is solely attributed to 
 inductance, At 90 degrees PA, the pure resistance of the wiring should have a 
 negligible effect.
 
 Therefore, what you should be looking for is impedance, or inductive 
reactance, 
 either in place of the dc wiring resistance or in addition to it. Once you've 
 considered this, the calculated results you get may be more in line with your 
 measured results.
 
 Just some humble opinions full of cobwebs. Good luck.
 
 Best regards,
 Ron Pickard
 [email protected]

______________________________ Reply Separator _________________________________
Subject: Inrush current and utility power line reistance 
Author:  <[email protected]> at INTERNET
List-Post: [email protected]
Date:    9/11/98 11:02 AM


 
 
From: John Garrett@HNS on 09/11/98 11:02 AM
 
 
To:   ieee pstc list <[email protected]> 
cc:
Subject:  Inrush current and utility power line reistance
 
Hello All,
 
I have a question with respect to the typical  resistance of the mains 
utility wiring; from the mains utility transformer into a residential or 
industrial building.  But first a little history on the problem:
 
When testing a 30 W power supply at 120VAC, the inrush current at a phase 
angle of 90 degrees measured 27A peak (4 unique sites were tested). 
Calculating inrush current is a fairly straight forward application of ohms 
law:
 
     Inrush Current = peak voltage divided by the dc resistance ( I = Vpeak
/ R)
(where R is the series resistance from the power line into the p/s through 
the EMI  filter through the rectifier and the bulk capacitor back out the 
other leg of the line)
 
In this application the result of the above equation is    I = (120 
VAC*1.414) / 3.00 ohms  or  I = 56.6 Amps... where 3  ohms is the worst 
case resistance internal to the power supply  (The assumption here being 
there is little if any resistance external to the power supply that will 
add significantly to this internal resistance).
 
 The problem is this: the calculated number (56.6 A) does not come close to
the measured (27A).  If fact, when we look at the measured data it appears 
as if the external resistance, i.e. the resistance of residential or 
industrial wiring from the utility mains transformer to the building and 
internal to the building, is adding a very significant amount of resistance 
(approx. 3.0 ohms).  This is very hard to believe!  But it is repeatable. 
We are checking these measurements even as I write, but my questions are 
simple.  First, am I missing something here with respect to second order 
effects?  Second, does anyone have a feel for the resistance of the power 
lines from the utility mains xfmr to the service entrance and into a 
residential or industrial building?  Have any studies been performed that I 
can refer to for this type of information?  Any help would be greatly 
appreciated.
 
 
 
 
John Garrett                  Principal Engineer 
Hughes Network Systems        Phone  (301) 601-2699
11717 Exploration Lane             FAX      (301) 428-2835 
Germantown, MD 20876               Email: [email protected]
 
 
 
---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected] 
with the single line: "unsubscribe emc-pstc" (without the 
quotes).  For help, send mail to [email protected], 
[email protected], or [email protected] (the list 
administrators).
 
 


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], or [email protected] (the list
administrators).

Reply via email to