Richard,

The caveat in Henry Ott's statement about 20 dB, are the words,
"properly designed."  For equipment that is not "properly designed," 20
dB may be a little on the lean side.  Boards that are not "properly
designed" are very common.

Since it is difficult to predict shielding performance (or shielding
need) with accuracy (see my previous posting), a cautious designer will
either over-design, or provide a contingency to add additional shielding
if the need arises. I have done the  latter and been very glad about it.


Jim
------------------------------------------------------------------------
---------------------------
Dr. Jim Knighten
NCR
17095 Via del Campo
San Diego, CA 92127
Telephone: 619-485-2537
Fax: 619-485-3788
e-mail: [email protected]


        ----------
        From:  WOODS, RICHARD [SMTP:[email protected]]
        Sent:  Tuesday, July 21, 1998 6:33 AM
        To:  'emc-pstc'
        Subject:  Designing Openings for EMC Compliance

        Thanks to all of you who replied to my request. I received at
least four
        different formulas ranging from the very complex to the very
simple. Some
        equations were based upon the wave guide beyond cutoff
principle, but some
        people said that the wave guide formula does not apply to thin
panels. Most
        people seem to rely upon a simple equation which can be found in
Henry Ott's
        book and other sources. The equation is based upon the
fact/assumption (your
        choice) that a slot dimension of 1/2 wavelength has zero loss.
The equation
        then becomes  A = 20 log (lambda/2L). For multiple apertures,
the reduction
        in shielding is approximately proportional to the square root of
the number
        of openings:  A = - 10 log n.

        Several people indicated that I should avoid using equations
with dB when
        addressing Mechanical Engineers and Designers, so I made the
equation even
        simpler. Henry Ott indicates that enclosures of properly
designed commercial
        equipment only needs 20 dB of shielding. I then added my own
assumptions.  I
        have assumed that the clock frequency is no higher than 33 MHz
which, based
        upon experience, can present harmonics up to about 600 MHz.
Therefore, I
        will design for 20 dB of shielding at 600 MHz. Using these
assumptions and
        combining the two equations above, one is left with the equation
L(cm) =
        2.5/sqr(N). Now this is an equation the Mechanical Engineers and
Designers
        can live with.

        Comments?

        Richard Woods