Check section 725 of the National Electrical Code.  Class 1 (CL1) wire must
be rated 600V. But I don't think your application is Class 1. That is a high
power signal application. Your cable may be able to qualify as CL2 or CL3,
both of which do not require a conduit. If you must run the cable in a riser
between floors then an "R" or "P" suffix is required. If the cable runs in a
air handling space (plenum) then the cable must have a "P" sufix. 

Richard Woods
Sensormatic Electronics
[email protected]
Views expressed by the author do not necessarily represent those of
Sensormatic.


> ----------
> From:         Eric Henning[SMTP:[email protected]]
> Reply To:     Eric Henning
> Sent:         Saturday, June 27, 1998 5:20 AM
> To:   [email protected]
> Subject:      signal wire  300V  600V?
> 
> We supply a piece of cabling between one of our fluid measurements
> meters (electronics with a remote sensor).  One wire supplies 45Vdc and
> three other wires are for signal level.  our instruction book states
> this bundeled cable must be installed 
> in conduit.  all wires used are used well within their specs.
> 
> my question is,  if this wire is run in its own conduit can it be rated
> 300V?  An inspector in Oregon is telling me it has to be 600V wire as he
> is calling it Cl I wire.
> 
> Any thoughts would be appreciated.
> 
> eric
> [email protected]
> 