Hi folks.

I need some help in the following issue:

We use in our machines adjustable speed power drive systems. They are
synthesizing
a three phase sine wave by PWM. They have a very high disturbance
potential,
especially from the cable to the motor. If this cable is shielded and
the
shield is correctly bonded at both ends, the disturbances induced in
other are
usually below the limits. It is very important to bond the shield
correctly.

Now the problem:
Some times it is necessary (for safety reasons) to galvanically
disconnect the motor
from the drive system. At that point disturbances are created because:
- an impedance is added to the shield path (return path for HF), thus
dramatically reducing the effectiveness of the shield.
- the inner conductor build a radiating loop
- disturbances are coupled into the coil of the contactor an thus spread
into the machine
- disturbances are coupled in the wires to the auxiliary contacts
- disturbances are coupled in other wires in the neighborhood

A possible solution would be a contactor having the power contacts in a
shielded enclosure and the coil and the auxiliary contacts outside the
shielded enclosure.

[ see http://ourworld.compuserve.com/homepages/dancau/contacto.htm for
image]

DOES ANYBODY KNOW A SUPPLIER FOR SUCH CONTACTORS ?

Another possible solution would be to place the contactor in a shielded
enclosure, bond the shield to the enclosure  and to filter all wires
going in and out (to the coil and to the auxiliary contacts). My
experience shows that the requirements to the filter for the coil are
very high. and thus expensive.

Any comments on this issue are welcome.

Thanks in advance


George



--
**************************************************************
* Dr. Georg M. Dancau             *  HAUNI MASCHINENBAU AG   *
* [email protected]             *  Manager EMC Lab         *
* TEL: +49 40 7250 2102           *  Kampchaussee 8..32      *
* FAX: +49 40 7250 3801           *  21027 Hamburg, Germany  *
**************************************************************
* home: Tel: +49 4122 99451       *  Hauptstr. 60a           *
*       Fax: +49 4122 99454       *  25492 Heist, Germany    *
**************************************************************



Reply via email to