>Hi folks.
>
>I need some help in the following issue:
>
>We use in our machines adjustable speed power drive systems. They are
>synthesizing
>a three phase sine wave by PWM. They have a very high disturbance
>potential,
>especially from the cable to the motor. If this cable is shielded and
>the
>shield is correctly bonded at both ends, the disturbances induced in
>other are
>usually below the limits. It is very important to bond the shield
>correctly.
>
>Now the problem:
>Some times it is necessary (for safety reasons) to galvanically
>disconnect the motor
>from the drive system. At that point disturbances are created because:
>- an impedance is added to the shield path (return path for HF), thus
>dramatically reducing the effectiveness of the shield.
>- the inner conductor build a radiating loop
>- disturbances are coupled into the coil of the contactor an thus spread
>into the machine
>- disturbances are coupled in the wires to the auxiliary contacts
>- disturbances are coupled in other wires in the neighborhood
>
>A possible solution would be a contactor having the power contacts in a
>shielded enclosure and the coil and the auxiliary contacts outside the
>shielded enclosure.
>
>[ see http://ourworld.compuserve.com/homepages/dancau/contacto.htm for
>image]
>
>DOES ANYBODY KNOW A SUPPLIER FOR SUCH CONTACTORS ?
>
>Another possible solution would be to place the contactor in a shielded
>enclosure, bond the shield to the enclosure  and to filter all wires
>going in and out (to the coil and to the auxiliary contacts). My
>experience shows that the requirements to the filter for the coil are
>very high. and thus expensive.
>
>Any comments on this issue are welcome.
>
>Thanks in advance
>
>
>George
>
>
>
>--
>**************************************************************
>* Dr. Georg M. Dancau             *  HAUNI MASCHINENBAU AG   *
>* [email protected]             *  Manager EMC Lab         *
>* TEL: +49 40 7250 2102           *  Kampchaussee 8..32      *
>* FAX: +49 40 7250 3801           *  21027 Hamburg, Germany  *
>**************************************************************
>* home: Tel: +49 4122 99451       *  Hauptstr. 60a           *
>*       Fax: +49 4122 99454       *  25492 Heist, Germany    *
>**************************************************************
>
>
>
>


Reply via email to