Check 29 CFR Chapter XVII, Paragraph 1910.339.

The definition of  "acceptable" to OSHA includes (paraphrased):

(i)     Listing, or
(ii)    Where no agency Lists the type of product, approval from the local
electrical inspector, or
(iii)   For custom designed equipment intended for a particular customer,
the manufacturer can test and document the safety of the equipment and make
the file available for inspection.

The latter is the technical way out.

Richard Woods

        ----------
        From:  Dick Grobner [SMTP:[email protected]]
        Sent:  Friday, November 19, 1999 9:38 AM
        To:  '[email protected]'

        Richard - Hello - I'm one of the many members on the emc-pstc forum.
I read
        your response back to Duncan regarding Regulatory Safety
requirements for
        the US. With regards to electrical equipment used in a manufacturing
setting
        - I had a small disagreement awhile back with one of our upper
management
        people. The disagreement was based on the fact that I stated
somewhere I
        read that  all electrical equipment used in the manufacturing
environment
        should carry a third party safety approval (i.e. UL). He stated that
this
        was not so. You stated in your reply that there was a technical way
out of
        this, but not recommended! Would you be welling too provide me a
detailed
        explanation of the way out? Please provide references if possible.
My stance
        has not changed - I still feel that all equipment should be approved
by a
        third party, for liability issues if nothing else. I just need a
little more
        backing on this one. Your comments will be appreciated!
        Thx   

---------
This message is coming from the emc-pstc discussion list.