Hello,

Put the sprinklers in.  Also, make sure they are 360 deg (i.e. spray up and
down) heads!!.

At a previous employer, we had a fire in a cone lined, shield room.  We had
sprinklers, but they were only 180 deg. (i.e. down).  The fire started when
some cones on the ceiling came loose and came into contact with a spot
light.  

The fire smoldered for quite some time, before the sprinklers went off.
This forced the smoke out the vent holes in the bottom of the room.  That is
when we noticed the fire.

Because the sprinklers were below the cones and did not spray up, the cones
just keeps on burning.  The fire went up and out the top ventilation opening
and into the building ceiling.  At about this time, the fire department
showed up and put the fire out.  As with most fires, the majority of damage
was from the water and the smoke.

Ned Devine
Entela, Inc.
Program Manager III
Phone 616 248 9671
Fax  616 574 9752
e-mail  [email protected] 


-----Original Message-----
From: Price, Ed [mailto:[email protected]]
Sent: Tuesday, November 16, 1999 9:22 PM
To: '[email protected]'
Subject: Shielded Enclosure Fire Hazard



Hi Listmembers!

My lab just had an annual inspection visit by our friendly fire hazard
inspector. Seems that after 4 successive years of inspections, I suddenly
failed this year. The reason is that my 24' x 35' x 10' modular shielded
enclosure doesn't have internal water sprinklers.

Now I'm all in favor of sprinklers; there's several in the ceiling of the
parent room that contains my enclosure. But that doesn't protect the
contents of the shielded enclosure. What if a fire started inside the
enclosure and then had time to grow? The parent room sprinklers might not be
able to stop the blaze then! Never mind that there's almost no fuel within
the enclosure; just fire-retardant rated anechoic foam and a 10' long table
made out of wood 4x4's.

So I don't suppose this is really about common sense. Has anyone recently
addressed the issue of fire protection within a shielded enclosure? Or
should I move right on to the sprinkler RFQ phase?

Regards,

Ed


:-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-)
Ed Price
[email protected]
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA.  USA
619-505-2780 (Voice)
619-505-1502 (Fax)
Military & Avionics EMC Services Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis
:-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-):-)


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to