Be careful -- the lightning tests (surge) are NOTHING like the IEC standards
for Europe. The AC line test is the same, but there are several telecom line
tests requring 10/1000, 10/360, and 2/10us waveforms at various voltages and
currents. Most tests are three terminal tests (tip & ring surged
simultaneously with respect to ground), but there are also 4-wire tests
(two, 3-wire pairs) and 12 pair tests. Additionally there is a 10/250us
impulse used for coaxial lines that is HUGE energy.......

Mike Hopkins
[email protected]

> -----Original Message-----
> From: tdonnelly [SMTP:[email protected]]
> Sent: Wednesday, January 06, 1999 9:11 AM
> To:   [email protected]
> Cc:   emc-pstc
> Subject:      RE: Bellcore GR1089
> 
> The standard GR-1089-CORE is available for purchase in electronic media at
> http://www.bellcore.com/BC.dynjava?BellcoreHomeHomeGeneralHome
> If you go into the into the Information Superstore and do a keyword search
> for
> GR-1089-CORE you get to the following summary:
> 
> Document Number GR-1089
> Issue Number 02
> Issue Date Dec 1997
> Product Type Industry Requirements And Standards (RS)
> Replaces TA-NWT-001089 Issue02
> Component of FR-2063, FR-440, FR-64
> ORDERING INFORMATION
> 
> ABSTRACT: This Generic Requirements (GR) document contains the
> Electromagnetic Compatibility (EMC) and electrical safety criteria, that
> in
> Bellcore's view, are necessary for equipment to perform safely and
> reliably
> in the environment of a Telecommunications Service Provider.
> Components of this product are:
> GR-1089-CORE
> 
> The cost is $350 and they accept the major credit cards.
> 
> As Gary indicated the EMC testing is significant but it also gets into
> electrical
> safety requirements. Also as Gary indicated equipment specified to meet
> this
> requirement
> often have to meet the Bellcore NEBS GR-63-CORE requirements. This
> standard
> covers
> such things as Operation Temperature and Humidity, Altitude, Heat
> Dissipation, Flame
> Resistance, Fire testing, Use of fire-resistant Material, Smoke
> Corrosivity,
> Equipment
> Shock, Earthquake, Vibration, Contamination. This standard itself is
> fairly
> extensive
> and if your customer is not asking for it I would not worry about it, but
> you should
> be aware of it. GR-63-CORE can be found at the Bellcore Site as well.
> 
> 
> 
> 
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]]On Behalf Of Gary McInturff
> > Sent: Tuesday, January 05, 1999 8:00 PM
> > To: 'Fred Waechter'; emc-pstc
> > Subject: RE: Bellcore GR1089
> >
> >
> >     You can get the standard through Bell Labs, Global engineering
> > documents may also have it. Its long and arduous. It extends the
> > FCC limits
> > down to 10 Khz or so and up to 10 GHz, You may be required to do some
> > radiated emissions testing in this range as well as conducted
> > emissions. The
> > where the FCC has limits they are pretty much the same for the 1089
> tests.
> > They rise above and below this points, but I haven't got the figures in
> > front of me.
> >     They required susceptability requirements for surge, and ESD etc
> > that sort of match the Heavy industrial standards for Europe.
> >     There is a heck of lot more to it than this - this is just a
> > ballpark figure. I would certainly recommend that you get at least that
> > standard and spend a grunch of time looking it over before you
> > make a guess
> > at whether the supply will meet or not.
> >     I would also ask the client why he wants these tests. If it is going
> > into end use equipment that is going into a telephone company premises
> the
> > end client may have other questions for you like earthquake protection
> and
> > fire protection. For the earthquake stuff heavy things like power
> supplies
> > are at risk - they like to keep moving after the shaker has tried
> > to change
> > directions. You may even have to physically burn the power supply
> > to observe
> > the flame and smoke production during and after the application of
> flame.
> > Typically requiring flame classifications of 94v0 and better or
> components
> > with an oxegen index greater than 25 (I think). If it is fixed
> > equipment the
> > flame rating could even go to UL94-5V.
> >     So lots to think about.
> >     Gary
> >
> >     -----Original Message-----
> >     From:   Fred Waechter [SMTP:[email protected]]
> >     Sent:   Tuesday, January 05, 1999 10:01 AM
> >     To:     emc-pstc
> >     Subject:        Bellcore GR1089
> >
> >     Hi all,
> >
> >     I'm a consultant to a power supply manufacturer on the west coast.
> > They
> >     have a potential customer who asked if a particular power supply
> > could
> >     meet Bellcore GR1089. Neither the factory or I are familiar with
> > this
> >     standard. Does anyone know what it refers to and/or where I can get
> > a
> >     copy of this standard?
> >
> >     Thanks in advance for your help.
> >
> >     --
> >     Fred Waechter
> >     Sr. Applications Engr.
> >     SMPS Consulting
> >     [email protected]
> >     Phone/FAX: 336-246-5236
> >
> >
> >
> >     ---------
> >     This message is coming from the emc-pstc discussion list.
> >     To cancel your subscription, send mail to [email protected]
> >     with the single line: "unsubscribe emc-pstc" (without the
> >     quotes).  For help, send mail to [email protected],
> >     [email protected], [email protected], or
> >     [email protected] (the list administrators).
> >
> > ---------
> > This message is coming from the emc-pstc discussion list.
> > To cancel your subscription, send mail to [email protected]
> > with the single line: "unsubscribe emc-pstc" (without the
> > quotes).  For help, send mail to [email protected],
> > [email protected], [email protected], or
> > [email protected] (the list administrators).
> >
> 
> 
> ---------
> This message is coming from the emc-pstc discussion list.
> To cancel your subscription, send mail to [email protected]
> with the single line: "unsubscribe emc-pstc" (without the
> quotes).  For help, send mail to [email protected],
> [email protected], [email protected], or
> [email protected] (the list administrators).

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to