Nick,

The following is information obtained from the Ceramite capacitor catalog.

Class X capacitors are used between Line and Neutral.

Class Y capacitors are used between Line or Neutral and Ground. 

IEC 384-14 Subclass Y Capacitors:
*       A capacitor of a type suitable for use in situations where failure
of the capacitor could lead to danger of electric shock.
*       Class Y capacitors are divided into sub-classes based on type of
insulation bridged and voltage ranges,
*       Subclass Y capacitors may be used in applications which require a
Subclass X rating.

Y1
Voltage=250 VAC  Type of insulation bridged=Double or Reinforced   Peak
Impulse Voltage Before Endurance Test=8 kV

Y2
Voltage=250 VAC  Type of insulation bridged=Basic or Supplementary   Peak
Impulse Voltage Before Endurance Test=5 kV

Y4
Voltage=125 VAC  Type of insulation bridged=Double or Reinforced   Peak
Impulse Voltage Before Endurance Test=2.5 kV

IEC 384-14 Subclass X Capacitors:
*       A capacitor of a type suitable for use in situations where failure
of the capacitor would not lead to danger of electric shock.
*       Class X capacitors are divided into sub-classes according to the
peak voltage of the impulses superimposed on the main voltage to which they
may be subjected to in service.

X1
Voltage=400 VAC   Peak Impulse Voltage in Service=2.5 to 4.0 kV
Application=High Pulse

X2
Voltage=400 VAC   Peak Impulse Voltage in Service=Up to 2.5 kV
Application=General Purpose


Hope this helps. If you need more information Ceramite's phone number is
414-377-3500 and their web site is www.ceramite.com. I'm sure they would be
more than happy to answer any additional questions.


Best regards,

Kurt Andrews
Compliance Engineer
Tracewell Systems, Inc.
567 Enterprise Dr.
Westerville, OH 43081
Ph. 614-846-6175
Fax 614-846-7791
Email: [email protected] 


        -----Original Message-----
        From:   Nick Williams [SMTP:[email protected]]
        Sent:   Wednesday, September 08, 1999 5:12 AM
        To:     [email protected]
        Subject:        Suppression capacitors


        I'd appreciate it if someone could confirm (and/or add to) the
following,
        which is my understanding of the application of the various classes
of
        supression capacitor:

        X2 -    suitable for applications where the supply is connected
directly
        across the capacitor but the appliance is not permanently connected;

        X1 -    Suitable for applications where the supply is connected
directly
        across the capacitor and the appliance is permanently connected;

        Y -     Suitable for applications where the capacitor is connected
        directly  between the supply and accessible conductive parts.
        These definitions are based on Clause 14.2 of EN60065 but any
references to
        other standards which apply would also be useful.

        Thanks

        Nick.

        ---------
        This message is coming from the emc-pstc discussion list.
        To cancel your subscription, send mail to [email protected]
        with the single line: "unsubscribe emc-pstc" (without the
        quotes).  For help, send mail to [email protected],
        [email protected], [email protected], or
        [email protected] (the list administrators).
        

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to