The standard which applies is IEC 60384-14 Fixed capacitors for 
use in electronic equipment-Part 14, Sectional Specification;
Fixed capacitors for electromagnetic interference suppression and 
connection to the supply mains.

I only have a draft in my possession. It states "Capacitor of Class X,
a capacitor of a type suitable for use in situations where failure
of the capacitor would not lead to danger of electric shock...divided
into 3 sub-classes according to the peak voltage of the impulses 
superimposed on the mains voltage to which they may be subjected 
in service."  

"Capacitor of Class Y, a capacitor suitable for use in situations where
failure of the capacitor could lead to danger of electric shock...
divided into 4 sub-classes Y1, Y2, Y3, and Y4."

I'm sure you could get lots of information from any filter manufacturer,
especially Schaffner, or from a capacitor manufacturere such as 
EVOX/RIFA. I can tell you now that it is a complicated subject that I
am not expert on, but I have a file of magazine articles, etc.
You only have to look at clause 1.5.6 Mains Capacitors of IEC 60950
to see how complicated it is. 

Nick - if you want me to send you copies of anything I have on the
subject, let me know your address, but anything I have goes back 
to around 1992, and the draft IEC 384-14 which became 
IEC 384-14: 1993.
Regards.
John Crabb, Development Excellence (Product Safety) ,     
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee, Scotland. DD2
3XX
E-Mail :[email protected]
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289.


> -----Original Message-----
> From: Nick Williams [SMTP:[email protected]]
> Sent: 08 September 1999 10:12
> To:   [email protected]
> Subject:      Suppression capacitors
> 
> 
> I'd appreciate it if someone could confirm (and/or add to) the following,
> which is my understanding of the application of the various classes of
> supression capacitor:
> 
> X2 -  suitable for applications where the supply is connected directly
> across the capacitor but the appliance is not permanently connected;
> 
> X1 -  Suitable for applications where the supply is connected directly
> across the capacitor and the appliance is permanently connected;
> 
> Y -   Suitable for applications where the capacitor is connected
> directly  between the supply and accessible conductive parts.
> These definitions are based on Clause 14.2 of EN60065 but any references
> to
> other standards which apply would also be useful.
> 
> Thanks
> 
> Nick.
> 

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to