Berri,

APC makes UPS's that pass the cap discharge test even with non linear
computer loads plugged in.  Your blanket statement that a UPS will not pass
the cap discharge test with computer loads is not true.  Whether or not the
UPS will pass is dependent on the design.  There is nothing inherent about
a UPS that will make it fail a cap discharge test with a computer load
plugged in.

Bill Burks



Please respond to "Berri" <[email protected]>

To:   [email protected]
cc:   [email protected] (bcc: Bill Burks/SDD/NAM/APCC)
From: "Berri" <[email protected]> on 08/18/99 08:14 PM GMT
Subject:  RE: UPS





If a UPS is being approved to UL1778, the backfeed test can be conducted
with a linear load if the UPS is specified for use with linear loads.  With
a linear load the UPS will not have any voltage on the plug pins when
running off batteries, but if a non-linear load (such as a computer)is
used,
there is a voltage on the plug pins (around 60 volts peak).

This creates a problem if your product is being approved to UL1950 and
incorporates a UPS.  It will not pass the capacitor discharge test and you
are responsible for fixing the problem in your unit in order to obtain
approval.



Berri Remenick
Safety Compliance Engineer
Washington Laboratories, Ltd.



-----Original Message-----
From: [email protected]
[mailto:[email protected]]On Behalf Of
[email protected]
Sent: Tuesday, August 17, 1999 1:43 PM
To: [email protected]
Subject: UPS





Hello all,
     I was wondering if anyone had a comment on the following:  Most
uninterruptible power sources (UPS) have a unique characteristic.  There
exists
an "energy"  (albeit small) on the outlet plug prongs even when the unit is
not
connected to the mains supply.   I have been told that it won't "Bite" you
(~3ma
@ 30-60vac) and that this is "caused by the continuous neutral incorporated
in
the unit which is required by UL".   Although it may not be "dangerous" by
the
letter of the law, my concern is that if someone should unknowingly receive
this
"tingle" the natural reaction is to pull away which has potential for
injury.
     First, is this the "norm"?  and How should a manufacturer of a piece
of
equipment which incorporates a UPS warn their customers of this?  Anyone
have
experience with this?

Thank you in advance,

Lisa



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).




---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).









---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to