UL 1778 and EN50091-1-1 require backfeed testing which is almost identical
to capacitor discharge testing. If a UPS has approvals, there is no hazard
available(required to be less than 30VAC after 2 seconds). The test is also
done while faulting the transfer relays(this makes sure that the
manufacturer detects the possibility of the hazard and indicates a UPS
failure and does not expose the user to the hazard). For Europe, the test
duration is 1 second and they even specify very stringent spacings for the
transfer relays(reinforced insulation between UPS output and power cord
pins).
I don't believe that any sort of warning is necessary. The standards do not
make us put these kinds of warnings on the UPS.Yes there is a little energy
left, but it has discharged by the time you remove the plug and actually
touch the pins. On older UPS(pre 1992?) this was not properly addressed so
perhaps you have heard about problems that have since been eliminated(we
are very aware of this issue as we are involved with the standards
organizations and we have helped to develop this requirement based on our
own observations) Please realize that my opinions are of course biased as I
work for a UPS manufacturer.



Please respond to [email protected]

To:   [email protected]
cc:    (bcc: Steve Williams/SDD/NAM/APCC)
From: [email protected] on 08/17/99 08:43 PM GMT
Subject:  UPS







Hello all,
     I was wondering if anyone had a comment on the following:  Most
uninterruptible power sources (UPS) have a unique characteristic.  There
exists
an "energy"  (albeit small) on the outlet plug prongs even when the unit is
not
connected to the mains supply.   I have been told that it won't "Bite" you
(~3ma
@ 30-60vac) and that this is "caused by the continuous neutral incorporated
in
the unit which is required by UL".   Although it may not be "dangerous" by
the
letter of the law, my concern is that if someone should unknowingly receive
this
"tingle" the natural reaction is to pull away which has potential for
injury.
     First, is this the "norm"?  and How should a manufacturer of a piece
of
equipment which incorporates a UPS warn their customers of this?  Anyone
have
experience with this?

Thank you in advance,

Lisa



---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).









---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to