Good Answer (with respect to the standards noted below). 

However, I would like to expand on this discussion, if I may, with regards
to
telecom equipment in a CO (Central Office) environment and meeting Bellcore
specifications (realize that typically equipment that will go into a CO
environment will also need to meet UL 19503rd ed.).

In the case of Bellcore NEBS GR-63, the content of smoke is measured with
regard to
'Oxygen rating index' (should be 28% or greater) during the Fire Resistance
testing. The previous version of the specification (TR-NWT-000063)
specifically measured all the content of the smoke to determine smoke
corrosivity. 
Although the current standard (GR-63) is relaxed, the RBOCs (Regional Bell
Operating Companies - becoming less numerous of late) reserve the right to
view the video tape of the fire test when considering a product, and if they
feel that the product is producing too much smoke (regardless of the oxygen
index) they become concerned.
They're concerned about bringing down a central office to 'clean' the
surrounding equipment from the corrosive elements of the smoke.

So those of you who will also need to meet the Bellcore NEBS requirements
(telecom equip to be located in a CO) in addition to UL1950 3rd Ed., this
will be a concern.

John A. Juhasz
Product Qualification &
Compliance Engr.

Fiber Options, Inc.
80 Orville Dr. Suite 102
Bohemia, NY 11716 USA

Tel: 516-567-8320 ext. 324
Fax: 516-567-8322 


-----Original Message-----
From: Rich Nute [mailto:[email protected]]
Sent: Wednesday, April 21, 1999 2:30 PM
To: [email protected]
Cc: [email protected]
Subject: Re: Excessive smoke




Hi Jeff:


>   If a component abnormal test generates excessive and sustained smoke
>   (several minutes), but does'nt breach reinforced or double insulation,
nor
>   emit flame from the enclosure, is it considered a failure?  Intuitively,
it
>   seems like it would be, because of toxicity, but I have been unable to
find
>   anything in the safety standards to support this.  I have checked EN
60950,
>   EN 50178, UL 1012, and CSA C22.2 No. 107.1.

For the purposes of product safety and compliance with safety
standards, smoke is a "permitted" emission during fault testing.

The safety issue is whether a safeguard is damaged or breached
due to the heat which produced the smoke.  If insulation is not
damaged (as per the hi-pot test), and excessive heat or flame 
does not breach the enclosure (as per the cheesecloth test), 
then the product is considered acceptable for the purposes of 
product safety.

Typically, product safety standards do not address the toxicity
of smoke.  This is because all smoke contains toxic materials.  
The only solution to smoke toxicity is to eliminate smoke, which
means eliminating all overheating situations.  Which is nearly
impossible.

However, any smoke from a product is likely create fear and
anxiety in the mind of the user and nearby persons.  Any smoke
in a clean room will likely be cause for scrapping all stock in
the clean room.

While smoke always contains toxic materials (e.g., carbon monoxide),
the concentration of the smoke (toxic material) in the volume of 
the room together with the room ventilation determines whether or 
not inhalation of the smoke is likely to cause an injury.  If the
volume of smoke is small compared to the volume of the room, then
it is likely the concentration of toxic material will be below the 
TLV (threshold limit value) for that material.  

So, it is a good idea (for the satisfaction of your customers) to
eliminate or reduce any significant smoke emissions that might 
occur during fault testing.


Best regards,
Rich



-------------------------------------------------------------
 Richard Nute                      Product Safety Engineer
 Hewlett-Packard Company           Product Regulations Group 
 AiO Division                      Tel   :   +1 619 655 3329 
                        Effective 6/12/99:   +1 858 655 3329
 16399 West Bernardo Drive         FAX   :   +1 619 655 4979 
                        Effective 6/12/99:   +1 858 655 4979
 San Diego, California 92127       e-mail:  [email protected] 
-------------------------------------------------------------




---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to