Hi Doug:
> My question is this, is it because the inverter has a low voltage input and
> they do not have to comply to a standard like EN61010 or UL1950, or is this
> something the manufacturers haven't addressed because no one has ever asked?
I don't think anyone but the manufacturers can answer your
question. It is certainly easy to say that because the unit
is rated for less than 50 V input, it is exempt from the LVD.
The inverter is essentially a UPS with an external battery
and without the monitoring and switchover features. So, the
applicable safety standards would be those for UPS.
In the USA, under the NEC, the inverter would be considered a
separately-derived source. The NEC requires such sources to
be grounded.
At 300 watts output and 12 volts, the input current would be
more than
P 300
I = ----- = ------- = 25 amperes
E 12
Assuming at least 60 watts consumed in the inverter operation,
input current would be 30 amperes!
So, one major safety issue is that of overheating (and fire) due
to normal and fault-mode currents.
Another major safety issue is the isolation of the 120 volts
from the 12 volts.
Yet another is that of grounding, both the neutral and protective
conductors, of the 120-volt source.
So, there are real safety issues with such an inverter.
Best regards,
Rich
-------------------------------------------------------------
Richard Nute Product Safety Engineer
Hewlett-Packard Company Product Regulations Group
AiO Division Tel : +1 619 655 3329
Effective 6/12/99: +1 858 655 3329
16399 West Bernardo Drive FAX : +1 619 655 4979
Effective 6/12/99: +1 858 655 4979
San Diego, California 92127 e-mail: [email protected]
-------------------------------------------------------------
---------