Peter, 

Here's my two cents ... 

Extraneous/non-electrical Conductive Part - 

 1  A conductive part that is not intended 
    to be part of ANY electrical circuit 
    (power or otherwise) of a device.  

 2. If removed from the device, does not 
    cause any degradation of electrical performance. 

 3. Has a high enough conductance so that if energized 
    with a single mode fault from the lines voltage 
    for device, would cause current to flow in excess 
    of 5 mA. 

Remove item #3 above for "Extraneous Conductive Part". 


On Wed, 17 Mar 1999, Peter E. Perkins wrote:
> I'm involved in a discussion concerning definitions...  wot's you
> opinion...  
> 
> Exposed conductive part: conductive part of equipment, which can be
> touched and which is not normally live, but which can become live when
> basic insulation fails.
> 
> Extraneous/non-electrical conductive part: conductive part not
> forming part of the electrical installation and liable to introduce an
> electric potential, generally the electric potential of a local earth.  
> 
> The issue is with the name of the last definition.  Is it clearer
> to call it an 'Extraneous conductive part' or call it a 'Non-electrical
> conductive part'?  Why do you prefer one name over the other?  
> 
> Keep those cards and letters coming, folks...  we'll tally the
> votes and let you know how it comes out...  

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to