At 09:30 AM 3/3/99 -0800, Allen Tudor wrote:
>Clause 5.4.4 of UL 1950, Third Edition specifies that in lieu of creepage
and clearance distance requirements for operational insulation, the
electric strength test for operational insulation (Table 18) can be used.
>
>Does anyone know how to calculate minimum distances between traces on a
printed circuit board that would allow one to pass the dielectric test at a
given voltage?  Or has anyone taken any empirical data that would shed
light on this topic?  Also, would trace width have an impact on the
dielectric test results?

This is highly empirical and best done with a 
hi-pot tester and some bare boards. 

You're talking about Paschen's Law. 

Paschen's Law:  Breakdown Voltage (BV) for uniform gaps

 V(kV)= 24.2Sh +6.1(Sh)^0.5  

where 
 V is the breakdown voltage in KV
 S=(293p)/760T
 h is electrode spacing in cm.
 p is pressure mm of mercury
 T is temperature in degrees Kelvin

At STP, S = 1 so 30KV/cm is pretty good 

This relationship does not work for all values of pressure.  
This is all greatly dependent upon the geometry of the 
two test points of concern.  I believe Paschen came up with 
this empirical equation with point probes.  I like to remember 
that 3M volts for 1 meter at STP (roughly). That still works 
with the above equation. 

But remember that the field about two *point charges* varies 
inversely with the square of the distance.  The field about 
two *line charges* varies inversely only with distance. So be 
careful fudging distances with traces. 

If we have 3MV @ 1m, then 3KV @ 1 mm which is roughly 40 mils. 
Double it for a x2 safety factor to 2 mm or 80 mils.  For 
reinforced insulation, it's a x2 yet again so that now you 
have a 4 mm or 160 mil separation.  Pick the safety factor 
that you want.  I'm just suggesting this.  I seem to remember 
something about wire mfrs build in a safety factor of x7 into 
the insulation, but I'm not sure about that.  

Now, take a look at UL-1950, Table 3, "Minimum Clearances for 
insulation i primary circuits, and between primary and secondary 
circuits ..."   

In the column for >150V, <= 300V with a transient of 2.5KV, 
you get a rough idea (agreed very rough idea) of how these 
numbers work out ...  

" Vrms = 300V, Op = 1.7, B/S = 2.0, R = 4.0 " 

Some of those clearance numbers look familiar when compared to 
working it out long hand in my paragraph above?  
You can bet they do.  

The trace width does not have an impact on dielectric testing if 
you're talking about two traces horizontally adjacent on the same 
layer of the board.  Traces vertically adjacent to each other will 
be a different story since the old standby FR-4 with a Dk = 4.7 
will increase the BV by a factor of roughly 4.7. 

But, again, do your own empirical evaluations on your own boards. 
It will prove to be invaluable information.  Hi-pot testing is 
one of the most common areas of safety testing failure. 


---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to [email protected]
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to [email protected],
[email protected], [email protected], or
[email protected] (the list administrators).

Reply via email to