Mark;
There are several standards.  One was mentioned before (IEC61000-3-3).  This
standard is vague on its application to inrush currents but most people
consider it also applies to inrush.  Committee work in process clarifies
this in the latest draft now out for vote.  Maybe the vote is complete by
now.  This draft leaves no doubt about its application to inrush current.
 
Another standard is IEC61000-3-5 titled: Limitation of voltage fluctuations
and flicker in low-voltage power supply systems for equipment rated current
greater than 16 A.
 
Another standard is IEC61000-3-11 titled:  Limitations of voltage changes,
voltage fluctuations and flicker in public low-voltage supply systems -
Equipment with rated current less than or equal to 75A and subject to
conditional connection.  This standard is in the FDIS stage and the voting
period ends early July.  Apparently this standard covers the entire range up
to 75A and includes the ranges of 61000-3-3 and 61000-3-5.
 
The above are so called emission standards and there in addition there are
immunity standards.    If you need information on immunity -please let me
know.

Dave George 
Unisys Corp. 
2476 Swedesford Road 
Malvern, PA  19355 
Tel:  1-610-648-3653 
Fax: 1-610-695-4700 

-----Original Message-----
From: Mark Gill [mailto:[email protected]]
Sent: Thursday, June 01, 2000 1:56 PM
To: '[email protected]'; [email protected]
Subject: RE: Looking for Inrush Current Standard



Don - 

I have not heard of such a standard.  Somewhat obvious, but general product
safety requirements state that the inrush current must be limited such that
overcurrent protection devices (either supplemental or branch circuit) are
not opened in the course of normal operation of the product.  This would be
the upper limit for inrush, and depends upon the characteristics of the
particular protector.  Normally this is an end-product requirement, as
compliance is affected by all passives and the particular supplemental
protection (if any) in front of the supply in the final product.  Unusually
large decoupling capacitors (bulk) can sometimes require special circuits to
limit the size of the inrush current.

I am a bit unsure about the limits you mention below, specifically for t>500
ms, as normal operation of all products falls within this range and can well
exceed this limit (infinite time implies steady state)!  I hope this helps.

Regards, 

Mark Gill, P.E. 
EMC/Safety/NEBS Design 
Nortel Networks - RTP, NC, USA 


        -----Original Message----- 
From:   [email protected] [SMTP:[email protected]] 
Sent:   Thursday, June 01, 2000 9:03 AM 
To:     [email protected] 
Subject:        Looking for Inrush Current Standard 




        I am looking for a standard or standards (IEC, EN or similar) which
contain 
inrush current requirements for power supplies. 
The standard might require the inrush to be: <20A for 50 us<t<1.5ms, <10A
for 
1.5ms<t<500ms, 0.6A for t>500ms. 

        Do any good standards exist on inrush current? 

        Thanks, 
Don MacArthur 



        ------------------------------------------- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 

        To cancel your subscription, send mail to: 
     [email protected] 
with the single line: 
     unsubscribe emc-pstc 

        For help, send mail to the list administrators: 
     Jim Bacher:              [email protected] 
     Michael Garretson:        [email protected] 

        For policy questions, send mail to: 
     Richard Nute:           [email protected] 


Reply via email to