Thanks for the information Horst.

Regards,

Mark Gill, P.E.
EMC/Safety/NEBS Design
Nortel Networks - RTP, NC, USA


> -----Original Message-----
> From: [email protected] [SMTP:[email protected]]
> Sent: Friday, June 02, 2000 1:53 AM
> To:   Gill, Mark [NCRTP:0S33:EXCH]
> Subject:      Re: Looking for Inrush Current Standard
> 
> Mark,
> 
> the IEC61204 defines inrush current limits. Also you might refer to
> NAMUR (a standard of the chemical industry in Europe). This standard
> defines peak inrush current less 15 times the input current.
> 
> With best regards
> Horst 
> 
> > Mark Gill wrote:
> > 
> > Don -
> > 
> > I have not heard of such a standard.  Somewhat obvious, but general
> > product safety requirements state that the inrush current must be
> > limited such that overcurrent protection devices (either supplemental
> > or branch circuit) are not opened in the course of normal operation of
> > the product.  This would be the upper limit for inrush, and depends
> > upon the characteristics of the particular protector.  Normally this
> > is an end-product requirement, as compliance is affected by all
> > passives and the particular supplemental protection (if any) in front
> > of the supply in the final product.  Unusually large decoupling
> > capacitors (bulk) can sometimes require special circuits to limit the
> > size of the inrush current.
> > 
> > I am a bit unsure about the limits you mention below, specifically for
> > t>500 ms, as normal operation of all products falls within this range
> > and can well exceed this limit (infinite time implies steady state)!
> > I hope this helps.
> > 
> > Regards,
> > 
> > Mark Gill, P.E.
> > EMC/Safety/NEBS Design
> > Nortel Networks - RTP, NC, USA
> > 
> >      -----Original Message-----
> >      From:   [email protected] [SMTP:[email protected]]
> >      Sent:   Thursday, June 01, 2000 9:03 AM
> >      To:     [email protected]
> >      Subject:        Looking for Inrush Current Standard
> > 
> >      I am looking for a standard or standards (IEC, EN or similar)
> >      which contain
> >      inrush current requirements for power supplies.
> >      The standard might require the inrush to be: <20A for 50
> >      us<t<1.5ms, <10A for
> >      1.5ms<t<500ms, 0.6A for t>500ms.
> > 
> >      Do any good standards exist on inrush current?
> > 
> >      Thanks,
> >      Don MacArthur
> > 
> >      -------------------------------------------
> >      This message is from the IEEE EMC Society Product Safety
> >      Technical Committee emc-pstc discussion list.
> > 
> >      To cancel your subscription, send mail to:
> >           [email protected]
> >      with the single line:
> >           unsubscribe emc-pstc
> > 
> >      For help, send mail to the list administrators:
> >           Jim Bacher:              [email protected]
> >           Michael Garretson:        [email protected]
> > 
> >      For policy questions, send mail to:
> >           Richard Nute:           [email protected]

Reply via email to