Ran across a new wrinkle on this issue.
The NEC in section page70-162 and table 310-17 does describe derating of
ampacity capacity for conductors with temperature
That is for normally current carrying conductors. - hot and neutral.
How about for grounding and bonding conductors?
I see section 250-95 basically says that the ground wire shall be the same
size as the feed wires. It also says that if the feed wires are adjusted in
diameter for voltage drop the equipment ground conductors shall be adjusted
proportionally - but no reference (here at least) for temperature.
I am wondering if the fact that the ground wire is not intended to be a
normal current path but rather a short term 'emergency cutoff mechanism', if
you will. As such it won't have current flowing along it long enough to be
adversely affected by a higher than 30 degree ambient and therefore required
to be derated for ambient.
Make sense to anybody.
Gary

PS I also have a question for a non-member. He is wondering if anyone has a
source for shielded power supply cords? I am also thinking that Europe hates
those things because many countries many not have a grounded outlet, or that
outlet is so far from earth ground that there is a significant impedance
along that path.
You can respond directly to [email protected]
<mailto:[email protected]> 


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to