Hi Kyle,
 
The flame ratings are actually all harmonized now. (FT, UL and NEC). 
Information about the comparisons between the ratings can be found in 
applicable UL and CSA standards, or in the NEC or the Canadian Electrical Code.
 
I also have seen some emails with some information that is slightly inaccurate, 
but common assumptions:
 
The NEC "P" ratings (i.e., CMP, CL2P, etc.) are NOT tested for low toxicity 
smoke. They are just tested for optical density of smoke emissions 
(visibility). A lot of CMP and CL2P cables out there are EXTREMELY toxic went 
burning. They just emit less visible smoke. The plastics used to reduce 
emissions and increase flame retardance produce highly toxic gasses.
 
There is a hierarchy of flame ratings that are spelled out in the UL/CSA 
standards, as well as the NEC and Canadian Electrical Code:
For example, From low to high per Article 725 of NEC:
 
VW-1(CL2X?? I forget!!) wiring from wall to unit, or in electrical conduit
CL2 (UL1581) Anywhere VW-1 is allowed, plus in Cable Trays (excpet in Risers or 
Plenums)
CL2R (UL 1666 ?? I forget) Anywhere CL2 and VW-1 are allowed, plus in Risers
CL2P (UL910) Anywhere CL2R, CL2, and VW-1are allowed, plus plenums.
 
In the NEC, CMX, CM, CMR and CMP can be substituted appropriately in Article 
725 above, as well as the appropriate level of Canadian FT-x ratings...
 
I hope this helps.
 
If you have any further questions, I will try to help..
 
BR,
 
Robert Tims 
Engineering Project Leader 
Software Product Integration 
Ericsson Internet Applications, Inc. 
145 Crossways Park Dr. W. 
Woodbury, NY 11797, USA 
Tel: 516-677-1138 
Fax: 516-677-1111 
Pager: 516-891-8358 
Email:[email protected] 

-----Original Message-----
From: Ehler, Kyle [mailto:[email protected]]
Sent: Thursday, October 04, 2001 11:09 AM
To: [email protected]
Subject: Wiring flame ratings



If I may ask a back to basics question. 

The country specific agency flame ratings for insulated 
wiring seem to not be harmonized.  Some materials such 
as limited current (signal) interconnect wiring are marked 
as VW-1 while others are marked with FT-1,2,3,4 or CL-2. 
VW nomenclature is a UL rating for wiring, while FT-x is a 
Canadian rating and test method, and CL2 is a NEC rating. 
Have I left any out? (;^) 

Is there such a thing as a cross reference table that 
indicates which is equivalent (and per application?) ?  
For example, FT4 = VW-1 = CL2 for vert./horiz. raceway? 

Inquiring minds... 

Kyle Ehler  KCOIQE 
< mailto:[email protected] <mailto:[email protected]> > 
Assistant Design Engineer 
LSI Logic Storage Systems Div. 
3718 N. Rock Road 
U.S.A.  Wichita, Kansas  67226 
Ph. 316 636 8657 
Fax 316 636 8321 