In a past life I used to flame test wire and cables.  Alot of this
information can be found in the NEC.  If you look in the section concerning
Class 1, class 2 and class 3 remote-control, signaling and power-limited
circuits, you can find the different wire and cable types and the tests that
they must pass to be listed as such.  For example a cable that passes the
UL1581 vertical tray flame test can be marked with CL2 or CL3.
 

Jim Sotherden 
Agency Coordinator/Test Engineer 
Technology Compliance Team 
GE Fanuc 
804-978-.6224 
804-978-5588 fax 


 

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, October 04, 2001 1:00 PM
To: [email protected]
Subject: RE: Wiring flame ratings


Sorry. I answered too quickly. CL2 cable comes in various types including
some that are tested for smoke, such as CL2P for use in air handling spaces.

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Thursday, October 04, 2001 12:27 PM
To: [email protected]
Subject: RE: Wiring flame ratings


VW-1 rated wire is tested for flammability while CL-2 cable is tested for
toxic smoke emissions.

-----Original Message-----
From: Ehler, Kyle [mailto:[email protected]]
Sent: Thursday, October 04, 2001 11:09 AM
To: [email protected]
Subject: Wiring flame ratings



If I may ask a back to basics question. 

The country specific agency flame ratings for insulated 
wiring seem to not be harmonized.  Some materials such 
as limited current (signal) interconnect wiring are marked 
as VW-1 while others are marked with FT-1,2,3,4 or CL-2. 
VW nomenclature is a UL rating for wiring, while FT-x is a 
Canadian rating and test method, and CL2 is a NEC rating. 
Have I left any out? (;^) 

Is there such a thing as a cross reference table that 
indicates which is equivalent (and per application?) ?  
For example, FT4 = VW-1 = CL2 for vert./horiz. raceway? 

Inquiring minds... 

Kyle Ehler  KCOIQE 
< mailto:[email protected] <mailto:[email protected]> > 
Assistant Design Engineer 
LSI Logic Storage Systems Div. 
3718 N. Rock Road 
U.S.A.  Wichita, Kansas  67226 
Ph. 316 636 8657 
Fax 316 636 8321 




-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]