This is a slightly older NEBS document, but I believe the requirement number
hasn't changed.

    Gary

 

4.5.3 Listing Requirements

R4-3 [22] All network equipment that is directly powered by commercial ac,

either through a hard-wire or plug-and-cord connection, shall be listed for

the purpose by a Nationally Recognized Testing Laboratory (NRTL).

R4-4 [23] Inverters that provide power to network equipment or to
convenience

receptacles shall be listed for the purpose by an NRTL.

R4-5 [24] Network equipment that is intended to be located on customer

premises shall be listed for the purpose by an NRTL.