Thank You so much Rich, Patricia, Mike, Jim, Ed, et al;

Please do continue to contribute your wisdom to this forum.

I spoke with my LES engineer and good friend at UL.  [a good friend at UL is
a handy thing!]
Someday I should expound on the usefulness of proper care and feeding of
your agency engineer..

In our discussions, I pointed out the grey area in 1950 2.6.2 & 2.7.4 [B]
related to the conditions 
of applicability (PAG), and that this modular product is deployed in a rack
mount environment 
where the mains cord is terminated in a polarized coupler (and disconnect
device) making it nearly 
impossible to reverse the mains.
In addition, the rack mount cabinet provides mains distribution to this
module through 
double side breakers.  I built my case on these two items and believe I can
get an approval
upon review.

I'm told the remaining problem with this UPS is it fails 61000-4-5 in our
lab, although it 
passes 801-5, and that it also fails conducted emissions when using QP->Avg
techniques.
I could be in for engineering a fire enclosure to contain wiring, coupler,
filter, suppressor, 
and while in the area, a double side breaker -and of course, the attendant
investigative redo.

Normally, this would be good reason for vendor rejection, or at least a
public drubbing in this
forum, but we are committed for the short term to use this vendor's product
and I cannot afford
to risk any relationships -for now.  The decision was never mine to make.  
And now we are in a familiar loop where the lab is used to re-engineer a
vendor's product 
that is CE marked.  Doh!!

Statue today, pigeon yesterday...

Thanks again,
kyle

my words, my opinions/mania...etc.
 



-----Original Message-----
From: Rich Nute [mailto:[email protected]]
Sent: Wednesday, August 01, 2001 4:30 PM
To: [email protected]
Cc: [email protected]
Subject: Re: Mains fusing





Hi Kyle:


>   I have a new product that includes an off the shelf UPS that is rated
for
>   230V ac operation and has an internal single pole circuit breaker on the
>   mains inlet.  We want to target this product world-wide.  The UPS
presently
>   is CB and certified to EN60950 european only.  For North America we want
it
>   to have UL1950, and to obtain this, UL is demanding the breaker be
double
>   pole.

This is an unusual situation.

On the one hand, the UPS, with single-pole overcurrent
protection, has a CB to EN 60950 for use in Europe where
most mains supply plug configurations are non-polar.
There is no control that the overcurrent protection will 
be in the live conductor.

On the other hand, the UPS, with single-pole overcurrent
protection, is denied UL certification for use in the
North America where UL requires polarization of both
the UPS overcurrent protection and the mains supply plug 
configuration.  There is a reasonable control that the 
overcurrent protection will be in the live conductor.

There is indeed something wrong with this picture.

My guess is that the certification engineer is invoking
Table 1, Case B (UL 1950, 3rd).  (As someone had already
suggested, you should verify this with your certification
engineer.)  Probably, this is because he knows that you 
are marketing your product worldwide.

Since you have a CB, you are qualified for Case B 
independent of your UL certification.  You should point
this out to your certification engineer.

I would ask UL to investigate the product under Case A.
UL can, at its discretion, investigate products to
specific provisions of their standard.  UL can invoke
paragraph D of the UL foreword to the standard.  You
can even ask UL to so note this construction in the
UL report. 

In my experience, these proposals should get you around
this situation.

If you are still unable to use the single-pole overcurrent
protection, I would go to another NRTL.


Good luck, and best regards,
Rich