Tania,
 
The -48V centralized DC power systems used in the central offices of
telecommunications companies are limited to 60 VDC or less under normal
operating conditions, including during charging of the batteries, and are
therefore considered to be SELV by definition.  See 3.6 of UL 60950.
 
Annex NAB clearly specifies that the connections to the centralized DC power
system must meet the requirements for primary circuits as specified in
section 3.2, however there are no requirements for disconnect devices or
overcurrent protection specified in this annex.
 
This equipment has operator replaceable fuses for over current protection on
the power inputs and has numerous overcurrent devices in the PC assemblies.
However, it does not have a disconnect device since it is intended for
installation into telecom racks with other equipment that is similarly
connected. 
 
A disconnect device is required for equipment connected to the AC mains, as
specified in 2.7 of UL 60950, however there no requirements for disconnect
devices for equipment connected to a secondary SELV source.
 
The centralized DC power systems installed in these restricted access
locations are provided with disconnect devices for overcurrect and fire
protection.  I'm not sure how you would specify
the short circuit protection requirements for these systems, since they are
not branch circuits covered under Article 240 of the National Electrical
Code.
 
Rick Meyette

-----Original Message-----
From: Tania Grant [mailto:[email protected]]
Sent: Wednesday, May 16, 2001 7:18 PM
To: Richard Meyette; '[email protected]'
Subject: Re: Disconnect Devices for Telecom Equipment


Rick,
 
A -48 volt source is considered a secondary circuit, but that does not
necessarily make it a SELV circuit.   I also don't believe that even if your
equipment installation should be proven to be powered by a SELV circuit that
the disconnect requirements of Section 2.6 do not apply.  Here is why.
 
Note that UL 60950 plainly states that connections to - and overcurrent
protection for -d.c. powered equipment needs to meet the same sections as
for a.c. main powered equipment.   It stands to reason, therefore, that
disconnection from whatever mains should also meet Section 3.4.3 (UL 60950)
or 2.6 (I presume UL1950. 3rd edition).   
 
Annex NAB.2  states that  "... connections to the centralized d.c. power
system are subject to the requirements for PRIMARY CIRCUITS and shall be in
accordance with 3.2 (AC MAINS SUPPLIES)".    Sections 2.7.1 and 3.2.1 in
Annex NAE which address requirements for d.c. powered equipment refer you
back to a.c. mains powered equipment.   Also, reading the standard as a
whole, Permanently connected equipment, whether a.c. or d.c., needs to meet
the stated requirements.   (All my references are to the UL 60950 edition.)
 
There are many reasons why it can be considered unsafe not to have immediate
access to a disconnect device for any equipment;-- a shock hazard being just
one of them.   Thus, equipment powered from a SELV circuit is still subject
to fire and/or an energy hazard.   For fixed equipment, the presumption is
that the disconnect device is in the building installation accessible to
trained service personnel and, therefore, the relaxed requirement to provide
this information in the installation manual.   
 
However, I have a larger concern.   If you don't have a MAIN disconnect
device in your d.c. powered equipment, something tells me that you probably
don't have a circuit breaker for overcurrent protection.   Annex NAE refers
you back to Section 2.7.1 which states that  "... If...PERMANENTLY CONNECTED
EQUIPMENT  relies on protective devices in the building installation for
protection, the equipment installation instructions shall so state and shall
also specify the requirements for short-circuit protection or overcurrent
protection, or, where necessary, for both."   
 
I strongly recommend a good read of the complete Annex NAE.   Note that UL
60950 has renumbered or reassigned the Section references;  the content,
however, has not changed from UL 1950 that I have noticed.
 
Tania Grant
[email protected] <mailto:[email protected]> 
 
----- Original Message -----

From: Richard Meyette
Sent: Wednesday, May 16, 2001 4:35 PM
To: '[email protected]'
Subject: Disconnect Devices for Telecom Equipment


Here's a question for you telecom experts: 

Paragraph 2.6.3 of UL 1950 (Third Edition) requires permanently connected
equipment, 
that is not provided with a disconnect device, to include a statement in the
installation 
instructions that an appropriate disconnect device shall be provided as part
of the building 
installation. 

Telecom equipment intended for connection to a -48V centralized DC power
system located 
in a central office is considered to be permanently connected equipment. 

However, the centralized DC power source is considered to be a SELV
secondary circuit. 

I don't think that this requirement would be applicable in this case, since
section 2.6 deals 
with the requirements for primary power isolation.  However, I am being told
otherwise. 

It is no big deal to provide the statement. I would just like to get some
clarification 
on how this requirement is applied to telecom equipment. 


Rick Meyette 
Terawave Communications 




  _____  

Get your FREE download of MSN Explorer at http://explorer.msn.com
<http://explorer.msn.com> 




Reply via email to