Cameron,

The issue may be associated with wire gauge as suggested by Bill Fleury.

If the cordage is a 3 core flexible supply cord and the conductors have a
cross sectional area of 0.5mm2 (0.5 square mm).  This is not allowed under
AS/NZS 3191 (see Note 2 to Table 2.17 of AS/NZS 3191).

It could also be associated with insulation as suggested by Ray Russell.

AS/NZS 3191 is "Approval and test specification - Electric flexible cords".
You can purchase with credit card and immediately download an electronic
copy from Standards Australia (www.stadnards.com.au).  No.  I am not getting
royalties from Standards Australia!  Only wish I were.

Best regards,
Kevin Richardson

Stanimore Pty Limited
Compliance Advice & Solutions for Technology
(Legislation/Regulations/Standards)
Ph:       02-4329-4070       (Int'l: +61-2-4329-4070)
Fax:      02-4328-5639       (Int'l: +61-2-4328-5639)
Mobile:  04-1224-1620       (Int'l: +61-4-1224-1620)
Email:    [email protected]
             ([email protected] - alternate email)


-----Original Message-----
From: [email protected] [mailto:[email protected]]On Behalf
Of Cameron O'phee
Sent: Wednesday, 2 May 2001 10:23 AM
To: 'EMC - PSTC Forum'
Subject: Australian power cable requirements.




Hi All,

I have a situation where the test house I normally use for safety will
accept SJT cordage for an internal power cable but a different test house
will not.  The power cable conducts 240v from one power supply to another,
with both supplies internal to the machine. The second test house insists
that the cordage must be H05VVF.  Consequentely, I would like to know the
difference in requirements between the US SJT cordage and European H05VVF.

Regards,

Cameron O'Phee.
EMC & Safety Precompliance.
Aristocrat Technologies Australia.


Telephone       : +61 2  9697 4420
Facsimile       : +61 2  9663 1412
Mobile           :  0418 464 016



----------------------
CONFIDENTIALITY NOTICE
----------------------
This email is intended only to be read or used by the addressee.
The information contained in this e-mail message may be confidential
information. If you are not the intended recipient, any use, interference
with, distribution, disclosure or copying of this material is unauthorised
and prohibited. Confidentiality attached to this communication is not waived
or lost by reason of the mistaken delivery to you.

If you have received this message in error, please delete it and notify us
by return e-mail or telephone Aristocrat Technologies Australia Pty Limited
on +61 2 9413 6300.

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.rcic.com/      click on "Virtual Conference Hall,"


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://www.rcic.com/      click on "Virtual Conference Hall,"


Reply via email to