Robert,
Very nice response. Well summarized. I am pushing for option 2,
disconnection of one of the many and test. Then repeat for all supplies. You
exactly state my reasoning in this option as well. The standard is trying to
protect against an inadvertent loss of the grounding or bonding connection
which would then leave a person to be the touch current ground path. But
with multiple power cords even the failure of a single ground connection
would not result in the loss of grounding wire, and the current would indeed
be directed to ground rather than the roughly 2 Kohm impedance of a person.
The standards already direct that only a single fault at a time can be
introduced to the test for compliance. Option 1 effectively introduces 1 for
each successive supply provided.
I am waiting for an answer from the safety agencies right now. I'll
let you know what I hear. As always that doesn't necessarily mean it will
get interpreted the same next time, but it certainly helps.
Thanks
Gary
PS. This will still take some thinking for the Nordic countries which have
deviations based on the fact that they don't expect to see a good ground
path in many instances.
-----Original Message-----
From: Griffin, Robert [mailto:[email protected]]
Sent: Wednesday, January 24, 2001 7:08 AM
To: [email protected]
Subject: RE: Looking at leakage current specs
Ron Pickard commented (questioned)
**
"Also, an interesting paragraph exists in 5.2.2. It states "Equipment
designed for multiple (redundant) power supplies shall be tested with only
one supply connected." How would one interpret this? Only one supply
connected and then the other, and then add the currents?"
**
I will not specifically comment on Ron's question but will pose another. One
of the problems we have today is that many products have multiple power
supplies that are not always considered redundant. IEC TC74 changed the
IEC60950 3rd Edition text to ?clarify? this requirement. All the IEC60950
3rd Ed. based standards now read:
Equipment which is designed for connection to multiple power sources, only
one of which is required at a time (e.g. for backup) shall be tested with
only one source connected.
Equipment requiring power simultaneously from two or more power sources
shall be tested with all power sources connected.
Perhaps that in itself helps Ron but... this text was debated prior to
release because it is still not clear in its intent for some applications.
There are at least 2 prevailing opinions (perhaps there are more). Multiple
AC connections are common with the use of smaller power supplies in larger
quantity within a products that might have 1 power supply providing backup
for several "required" power supplies (2+1 or 3+1 protection schemes). Many
designs included AC filtering at each power supply and overall product
leakage currents (touch and protective earth currents as they are now known)
are perhaps increasing along with the number of mains connections. Now we
approach this from at least 2 ways ....
Opinion 1 - You should test the system with all the "required" power
supplies collectively by testing the loop from all the AC mains to any
accessible collective earthing connections. Effect = Sum the touch/PE
currents from each required source and the sum of all required sources shall
not exceed the limits.
Opinion 2 - With more than one power supply required to be connected, then
the product has multiple "required" earthing connections. Test for the
touch/PE currents from each power supply with the other supply connected to
the mains (including its earthing connection). Any measurable
touch/protective earth connection would flow through the 2nd earthing path.
Effect = The product's chassis is earthed through the second required power
supply, the measurable touch/PE currents will be negligible and the test
quite easy to pass regardless of the limits.
So... Is the requirement intended to capture and limit the increasing
leakage currents as the number of power supplies per product grows. OR is
the requirement intended to give credit (and latitude) to a product that has
required multiple earthing connections? It will be interesting to see where
this goes as the 3rd Edition standard's use becomes more widespread.
Bob Griffin
Compaq Computer Corp.
[email protected]
-----Original Message-----
From: David Gelfand [mailto:[email protected]]
Sent: Monday, 22 January, 2001 12:25 PM
To: [email protected]
Subject: Re: Looking at leakage current specs
As I understand it, a truly redundant power supply system means that only
one
supply is connected and working at a given time. In this case you can
measure
the leakage current from only one supply.
Our system uses two power supplies that share the load, if one dies, the
other
can maintain the full load. In this case the leakage current is measured
with
both supplies connected.
I think the way to approach this is, what happens if there is no protective
earth? In test 5.2.3 and 5.2.4, there is no permanent earth connection to
the
EUT. Any current leaking to the chassis can be shunted to ground through
someone touching it. This current must be less than 3.5 mA.
My CSA rep accepts the permanent ground connection, but management does not
like
the warning. We are also working with the manufacturer to reduce the
leakage
current on each supply.
Best regards,
David.
----- Original Message -----
From: "Ron Pickard" <[email protected]>
To: "Gary McInturff" <[email protected]>
Cc: <[email protected]>
Sent: Friday, January 19, 2001 3:42 PM
Subject: RE: Looking at leakage current specs
Gary,
>If this equipment has a chassis bonding connection like you find in
>telephone line up equipment, would then it fall under the class B
pluggable.
>I can still remove power cords, but have a chassis to frame bonding wire in
>parallel to that. (Yes, I know most of that stuff is DC but there is a
small
>number that is not). I hope to work with the power supply folks to reduce
>the problem through filter design if I can, but I think this is an
>interesting questions. What do you think?
Pluggable Type B is a term which only refers to an industrial type power
plug.
Having a permanently connected earthing connection may provide the relief
from
the excessive leakage
currents you're experiencing. Such a connection might be described in
6.3.3.2,
6.3.4.1 and 6.3.4.3.2
(yeah I know, these are telco references), but, they adequately describe the
earthing conditions and
requirements. As an aside (well, sort of) I could never understand why such
a
protective earthing
connection is described for the protection of a telecom circuit, and not
mentioned at all for the
protection (leakage current, etc.) of an AC mains circuit. Maybe someone
more
knowledgeable than I
can explain that. At any rate, pass this by your friendly NRTL for their
interpretation of doing
this.
Also, an interesting paragraph exists in 5.2.2. It states "Equipment
designed
for multiple
(redundant) power supplies shall be tested with only one supply connected."
How
would one interpret
this? Only one supply connected and then the other, and then add the
currents?
Again, maybe someone
more knowledgeable than I can explain this.
Just trying to stir the pot.
Best regards,
Ron Pickard
[email protected]
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Jim Bacher: [email protected]
Michael Garretson: [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Jim Bacher: [email protected]
Michael Garretson: [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Jim Bacher: [email protected]
Michael Garretson: [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]
-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.
To cancel your subscription, send mail to:
[email protected]
with the single line:
unsubscribe emc-pstc
For help, send mail to the list administrators:
Jim Bacher: [email protected]
Michael Garretson: [email protected]
For policy questions, send mail to:
Richard Nute: [email protected]