Actually since you mention it my application for cable cm CE control covered
the spectrum from 150 kHz to 200 MHz!  But the application was
aerospace-related.  I have to say, however that I think an I/O cable would
be driven by PCB ground noise, which would be clock-speed related, not power
supply switching-speed related.

Ken Javor

----------

----------
>From: "Ralph Cameron" <[email protected]>
>To: "Ken Javor" <[email protected]>, "David Heald"
<[email protected]>, "Tudor, Allen" <[email protected]>
>Cc: "EMC-PCST \(E-mail\)" <[email protected]>
>Subject: Re: Site Correlation
>Date: Sun, Jan 14, 2001, 7:57 AM
>

> Ken:
>
> I like the idea of setting a limit to common mode currents on attaching
> cables but mI wonder why CISPR has chosen to start such measurements at
> 30Mhz when most of the common mode currents are the result of switching
> products and are generated harmonically from the fundamental  and as such
> propagate from the low Khz range up through 30Mhz. is there no consideration
> for those who occupy the spectrum below 30Mhz?
>
> In my applications of common mode suppression, almost every case, the source
> generating the common mode currents , when suppressed with simple external
> common mode chokes, satisfactorily reduced all the localized radiation
> caused by such effects.
>
> Series common mode chokes not only suppress the outgoing but reduce the
> incoming common mode currents that have the same potential for casuing
> equipment malfunction.
>
>
> Ralph Cameron
> EMC Consulting and Suppression of Consumer Electronic Equipment
> (After Sale).
>
> ----- Original Message -----
> From: "Ken Javor" <[email protected]>
> To: "David Heald" <[email protected]>; "Tudor, Allen"
> <[email protected]>
> Cc: "EMC-PCST (E-mail)" <[email protected]>
> Sent: Saturday, January 13, 2001 3:43 AM
> Subject: Re: Site Correlation
>
>
>>
>> I must say that this thread has been a refreshing alternative to the
>> EMC-law/regulations questions that typically occupy this service.  Not
>> complaining either, because If I suddenly found myself working commercial
>> EMC issues I would likely be flooding this line with those self-same
>> questions.
>>
>> Almost as an aside, Mr. Heald raises an issue of enduring interest to
> myself
>> and others.
>>
>> "Another important factor... is to manipulate the cables during testing
> (oh,
>> how much easier our job would be without  cables)."
>>
>> The same issue was raised parenthetically in my answer to the question
> about
>> GTEM polarization. The issue is control of cable-sourced  radiated
>> emissions.  I am now about to allegorically take a baseball bat to a
>> hornets' nest...
>>
>> Bela Szentkuti pointed out almost twenty years ago that it would be much
>> more efficient and accurate to analytically/experimentally determine the
>> relationship between cable common mode currents and the resultant radiated
>> field based on the maximum possible radiation efficiency of that cable,
> and
>> use that relationship to derive a common mode current limit for cables
> from
>> 30 MHz to 1 GHz, using the absorbing clamp as a measuring tool.  This
> would
>> speed up OATS or any other kind of RE testing by deleting the requirement
> to
>> maximize cable radiation.
>>
>> So this question is a poll.  How do the subscribers to this service feel
>> about cable common mode current control in lieu of direct measurement of
>> cable-sourced RE measurement?  The idea being that first you would measure
>> and bring cable cm CE into compliance with a cable-type limit and only
> then
>> would you make the RE measurement.  The cables would only be support
>> equipment which did not contribute to the RE profile, hence any measured
>> emissions at or near the limit would be guaranteed EUT enclosure-related.
>>
>> Polite responses only, please!!!
>>
>> Ken Javor
>>
>>
>>
>> ----------
>> >From: David Heald <[email protected]>
>> >To: "Tudor, Allen" <[email protected]>
>> >Cc: "EMC-PCST (E-mail)" <[email protected]>
>> >Subject: Re: Site Correlation
>> >Date: Fri, Jan 12, 2001, 9:36 AM
>> >
>>
>> >
>> > Greetings again.
>> >    I received some questions about this off list and there has been more
>> > discussion in this direction, so I thought I would throw my other two
>> > cents in.
>> >    For small fully anechoic chambers with little room for antenna height
>> > adjustment, you should be able to have uncertainty of about 6dB or so
>> > (10dB is much safer realistically) when you apply correction factors for
>> > a 10m site.  The reason for this is, as John Barnes pointed out, the
>> > absence of reflected waves being received in addition to the direct
>> > waves.  The key importance to a fully lined chamber (including the
>> > floor) is that destructive waves are not present.  With a reflective
>> > floor, destructive waves can lower your readings by more than 30dB.  Add
>> > this to the 6 dB or so of uncertainty for additive waves and your total
>> > error could be enormous.  With an absorber lined floor, the influence of
>> > the destructive waves is eliminated or reduced, so a correlation of 6dB
>> > (again 10dB is safer) should be achievable (this simply accounts for the
>> > absence of constructive interference).
>> >    Another important factor to ensure you don't have any surprises when
>> > moving from precompliance to a compliance run is to manipulate the
>> > cables during testing (oh, how much easier our job would be without
>> > cables).  Large signal strength changes can be achieved just by moving
>> > cables a few inches.
>> >    I also have to agree with Gert's and Ken's comments on far field
>> > measurements.  I mentioned this in my original message, but didn't
>> > elaborate at all.  These are very important considerations that can
>> > greatly affect any expected correlation to a 10m OATS.
>> >
>> > --
>> > David Heald
>> > Senior EMC Engineer/
>> > Product Safety Engineer
>> >
>> > Curtis-Straus LLC     NRTL
>> > Laboratory for NEBS, EMC, Safety, and Telecom
>> > Voice:978.486.8880x254   Fax:978.486.8828
>> > www.curtis-straus.com
>> >
>> >
>> > Tudor, Allen wrote:
>> >
>> >> Greetings:
>> >>
>> >> What's the best way to correlate a pre-compliance chamber (smaller than
> a 3m
>> >> chamber) to a 10m anechoic chamber?  Should I use a signal generator
> and
>> >> antenna or should I use a comb generator?
>> >>
>> >> Would the answer be different if I were correlating the pre-compliance
>> >> chamber to an OATS?
>> >>
>> >> Thanks in advance.
>> >>
>> >>
>> >> Allen Tudor, Compliance Engineer
>> >> ADC DSL Systems Inc.
>> >> 6531 Meridien Dr.
>> >> Raleigh, NC  27616
>> >> phone: 919.875.3382
>> >> email: [email protected]
>> >>
>> >>
>> >> -------------------------------------------
>> >> This message is from the IEEE EMC Society Product Safety
>> >> Technical Committee emc-pstc discussion list.
>> >>
>> >> To cancel your subscription, send mail to:
>> >>      [email protected]
>> >> with the single line:
>> >>      unsubscribe emc-pstc
>> >>
>> >> For help, send mail to the list administrators:
>> >>      Jim Bacher:              [email protected]
>> >>      Michael Garretson:        [email protected]
>> >>
>> >> For policy questions, send mail to:
>> >>      Richard Nute:           [email protected]
>> >>
>> >>
>> >>
>> >>
>> >
>> >
>> >
>> > -------------------------------------------
>> > This message is from the IEEE EMC Society Product Safety
>> > Technical Committee emc-pstc discussion list.
>> >
>> > To cancel your subscription, send mail to:
>> >      [email protected]
>> > with the single line:
>> >      unsubscribe emc-pstc
>> >
>> > For help, send mail to the list administrators:
>> >      Jim Bacher:              [email protected]
>> >      Michael Garretson:        [email protected]
>> >
>> > For policy questions, send mail to:
>> >      Richard Nute:           [email protected]
>> >
>> >
>>
>> -------------------------------------------
>> This message is from the IEEE EMC Society Product Safety
>> Technical Committee emc-pstc discussion list.
>>
>> To cancel your subscription, send mail to:
>>      [email protected]
>> with the single line:
>>      unsubscribe emc-pstc
>>
>> For help, send mail to the list administrators:
>>      Jim Bacher:              [email protected]
>>      Michael Garretson:        [email protected]
>>
>> For policy questions, send mail to:
>>      Richard Nute:           [email protected]
>>
>>
>>
> 

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Jim Bacher:              [email protected]
     Michael Garretson:        [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]

Reply via email to