Summary ===========================

The EC "ozone regulation" No. 2037/2000 does, indeed, prohibit the use of
HCFC's as early as 1/1/00. In fact, some uses of HCFC's as early as 1/1/96.
The trick to reading this regulation is to understand that the prohibition
dates are scheduled according to the use of the HCFC. There are different
dates, for example, for HCFC's used as solvents, aerosols, and refrigerants.
The refrigerant use is, itself, broken down into different use sectors (i.e.
Military Vehicles, Public Transport Air-conditioning)....

Before you can determine when your products use of HCFC will be prohibited,
you must determine how the regulation speaks of your product...not always an
easy task.

Since the regulation is focused on the EU it is more difficult to find the
language pointed towards manufacturers outside the EU who are selling into
the EU. Note, for example, that "producer" in this document means a producer
of HCFC (or other banned material), NOT a producer of equipment that
utilizes the material. (ref article 2).

As with most EU legislation, the primary burden of compliance is on those
people in the union. Therefore, the burden is on the importer of equipment
utilizing banned materials, not specifically on the exporter outside the EU.
Of course, many US based companies have a Euro affiliate, and share
reputation and "bottom line" or have contractual agreements not to get the
Euro guys in trouble with "the law."

Also note that this regulation seems to include reporting requirements for
those who IMPORT HCFC's and related materials into the EU. Article 4 and or
Article 6 describes this. So if you export equipment that utilizes HCFC's,
but it is imported EMPTY of the HCFCs, you are pretty clear of obligations.
However if you export HCFC containing equipment, even during the period
before prohibition for your particular product, the importer of your
equipment probably has reporting responsibilities. 

The body that must receive these reports, and how import quota's are
determined are unclear to me at this time. I need to re-read the regulation
10 or so more times. 

Attached is an analysis I did for a "chiller" that uses HCFC's in its
primary cooling cycle against the prohibition requirements of article 5. It
is a specific case study, but may be useful to you. 

 <<Analysis of CFC directive.doc>> 

I do not know how a "regulation" is different from a "directive." - more to
learn !

The two amendments to this regulation to not change the base document in a
large way. 

Details ===========================================
Found by searching at "Directory of Community legislation in force"
(http://europa.eu.int/eur-lex/en/lif/ind/en_analytical_index_15.html) with
key word "2037/200) selecting 'legislation in force' and 'consolidated
legislation' check boxes on search page. 


The basic act  http://europa.eu.int/eur-lex/en/lif/dat/2000/en_300R2037.html

A first amendment
http://europa.eu.int/eur-lex/en/lif/dat/2000/en_300R2038.html

A second amendment
http://europa.eu.int/eur-lex/en/lif/dat/2000/en_300R2039.html

Lauren Crane
*       Principal Safety & Compliance Engineer
*       Ion Beam and Thermal Processing Systems
*       Axcelis Technologies Inc. 
*       108 Cherry Hill Dr. 
*       Beverly, MA  01915
*       978.787-9745   [email protected]

Attachment: Analysis of CFC directive.doc
Description: MS-Word document

Reply via email to