Ghery -

He is correct.  There are DELTA configured transformers with
one phase earthed in the US.  This is referred to as "corner
grounded."

Refer to

http://saskpower.apogee.net/foe/ftdttd.asp

for a brief on the applications.  The site is incomplete
(overall), but has some useful information.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]]On Behalf Of
Pettit, Ghery
Sent: Monday, December 17, 2001 8:01 AM
To: '[email protected]'; Crabb, John; 'Bill Lawrence';
'EMC-PSTC Forum'
Subject: RE: Three phase delta system in USA


Horst,

Not correct.  From past experience, the 480 VAC 60 Hz delta
system runs with all three phases floating.  This is also
done on ships so that a fault to ground on a single phase
does not disrupt the system.

Ghery Pettit
Intel

-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Monday, December 17, 2001 6:05 AM
To: Crabb, John; 'Bill Lawrence'; 'EMC-PSTC Forum'
Subject: Three phase delta system in USA


I also learned, that there is a three-phase delta system in
USA with 500 Vac per phase.
One phase (L3) is earthed.

Is this system very often used in USA?
Is it correct information, that L3 is always earthed and not
L1 or L2.

Horst Haug

-----Ursprüngliche Nachricht-----
Von: [email protected]
[mailto:[email protected]]Im Auftrag von
Crabb, John
Gesendet: Montag, 17. Dezember 2001 11:28
An: 'Bill Lawrence'; 'EMC-PSTC Forum'
Betreff: RE: 2 Phases in North America

Bill - you absolutely correct in describing the North
American system as
"single-phase, 3 wire". After all, that is how it is
described in Annex V,
Figure V.4 of IEC60950:1999 - and there is NO WAY that IEC
TC74
could be wrong, is there ? (especially since the US
committee must
have voted yes, to include this change, the purpose of which
was to
educate those of us who weren't too clear on the subject).

Fortunately I am on holiday (vacation) from tonight until
January 3,
so to all our readers, best wishes for the Christmas season,
and a
happy and prosperous 2002.
John Crabb, Development Excellence (Product Safety) ,
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee,
Scotland. DD2 3XX
E-Mail :[email protected]
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.
VoicePlus  6-341-2289.
-----Original Message-----
From: Bill Lawrence [mailto:[email protected]]
Sent: 14 December 2001 22:33
To: 'Wagner, John P (John)'; 'Robert Johnson'; 'Cortland
Richmond'
Cc: 'Barry Esmore'; 'EMC-PSTC Forum'
Subject: RE: 2 Phases in North America
Two Phase / 5 Wire (4 "hots" and a neutral) was a common
power distribution in US cities in the early part of this
century.  Many early motors are "2-phase" motors.  I learned
about this when helping with connection of these motors to
run on a 3 phase power system via a special "Scott-T"
transformer connection.

The correct designation for the 120/240 power system
described is "Single Phase / 3 Wire".

Bill Lawrence


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        [email protected]
     Dave Heald                [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    No longer online until our new server is brought online and the old 
messages are imported into the new server.

Reply via email to