Horst,
 
Not correct.  From past experience, the 480 VAC 60 Hz delta system runs with
all three phases floating.  This is also done on ships so that a fault to
ground on a single phase does not disrupt the system.
 
Ghery Pettit
Intel
 
-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Monday, December 17, 2001 6:05 AM
To: Crabb, John; 'Bill Lawrence'; 'EMC-PSTC Forum'
Subject: Three phase delta system in USA


I also learned, that there is a three-phase delta system in USA with 500 Vac
per phase. 
One phase (L3) is earthed. 
 
Is this system very often used in USA? 
Is it correct information, that L3 is always earthed and not L1 or L2. 
 
Horst Haug 
 
-----Ursprüngliche Nachricht-----
Von: [email protected]
[mailto:[email protected]]Im Auftrag von Crabb, John
Gesendet: Montag, 17. Dezember 2001 11:28
An: 'Bill Lawrence'; 'EMC-PSTC Forum'
Betreff: RE: 2 Phases in North America
 
Bill - you absolutely correct in describing the North American system as 
"single-phase, 3 wire". After all, that is how it is described in Annex V,
Figure V.4 of IEC60950:1999 - and there is NO WAY that IEC TC74
could be wrong, is there ? (especially since the US committee must
have voted yes, to include this change, the purpose of which was to
educate those of us who weren't too clear on the subject).
 
Fortunately I am on holiday (vacation) from tonight until January 3,
so to all our readers, best wishes for the Christmas season, and a 
happy and prosperous 2002.
John Crabb, Development Excellence (Product Safety) ,     
NCR  Financial Solutions Group Ltd.,  Kingsway West, Dundee, Scotland. DD2
3XX 
E-Mail :[email protected] 
Tel: +44 (0)1382-592289  (direct ). Fax +44 (0)1382-622243.   VoicePlus
6-341-2289. 
-----Original Message-----
From: Bill Lawrence [mailto:[email protected]]
Sent: 14 December 2001 22:33
To: 'Wagner, John P (John)'; 'Robert Johnson'; 'Cortland Richmond'
Cc: 'Barry Esmore'; 'EMC-PSTC Forum'
Subject: RE: 2 Phases in North America
Two Phase / 5 Wire (4 "hots" and a neutral) was a common power distribution
in US cities in the early part of this century.  Many early motors are
"2-phase" motors.  I learned about this when helping with connection of
these motors to run on a 3 phase power system via a special "Scott-T"
transformer connection.
 
The correct designation for the 120/240 power system described is "Single
Phase / 3 Wire".
 
Bill Lawrence

Reply via email to