NEC Wiring QuestionMichael,

The 1996 version of the NEC addresses this issue by saying that if a
connector is not specifically listed for an application, it is not OK. The
reference is: 300-15(c) - "Fittings & Connectors shall be used only with the
specific wiring methods for which they are designed and listed."

IMHO, this means that unless the device, connector, terminal is specifically
listed for use with multiple wires of different sizes in the same hole, then
it is not allowed. At Fluke, when I was working with IEC 61010 and UL 3111,
our standard practice was that one terminal location could have one wire.
Connector and terminal block manufacturers make bridging or shorting bars to
connect multiple terminals together. The rationale is that multiple wires in
a terminal can work themselves loose over time and with stress.

Best regards,

Daniel E. Teninty, P.E.
Managing Partner
DTEC Associates LLC

(509) 443-0215
(509) 443-0181 fax
http://www.dtec-associates.com

Streamlining The Compliance Process
While Advancing New Products To Market

This email transmission is confidential and intended for the addressee only.
It may contain privileged and confidential information. If you are not the
person or organization to whom it is addressed, you must not copy,
distribute, or take any action in reliance upon it.


  -----Original Message-----
  From: [email protected]
[mailto:[email protected]]On Behalf Of Michael Taylor
  Sent: Wednesday, May 08, 2002 10:15 AM
  To: [email protected]
  Subject: NEC Wiring Question


  Greetings all,
  An issue came up in a product 61010 safety evaluation and no one here can
remember if you can / can't do it.
  Does anyone out in Cyberland know if the NEC allows 2 wires of different
sizes (awg) to be clamped together in a clamping type PC mounted wiring
terminal.

  The wire is striped bare & inserted into a slot on the side of a terminal
block that has a screw on top for tightening.

  I seem to remember the code does not allow wires of different gauges to be
clamped together under a single compression clamping terminal.

  I have searched the NEC and can't find anything on this.
  Can anyone remember chapter & verse on this issue.
  If I'm wrong, please be kind, the 60 hour weeks are getting to us.
  Thanks in advance
  Michael Taylor
  Colorado