Vijay,

I have posted my opinions within brackets [   ]  in your note below.




"Wani, Vijay (V)" <vwani%[email protected]> on 04/20/2002 08:38:51
PM

Thank you all for your valuable input. i apologize for late reply. i ordered
a copy of EN60950:2000. (thanks, Chris, George and constantin) and now, it
is getting much clearer. however, i have some questions and would appreciate
any comment.

as per EN60950:2000, 4.7.2.1:
1.   Except where method 2 of 4.7.1 is used exclusively, or as permitted
in 4.7.2.2, the following parts are considered to have a risk of ignition
and, therefore, require a FIRE ENCLOSURE:
- components in PRIMARY CIRCUITS;

So if i am interpreting Rich and Scott's e-mail right (great explanation),
i do not need FIRE ENCLOSURE, if primary circuit is supplied by a Limited
Power source.   For an existing device, how do i know whether the primary
circuit is supplied by a Limited Power source?  are cell-phones, PDA's
typically supplied by Limited Power Source?

[The type devices you list are typically battery powered.  The output of
batteries can often be totally unlimited, thus fire hazards.  However, a
current limiting device may be used to obtain a "limited power source".
One way to determine what is the case is to buy the product and test the
battery power to the conditions for limited power source.]

as per 4.7.3.4
2.   Inside FIRE ENCLOSURE, materials for components and other parts,
(including MECHANICAL and ELECTRICAL ENCLOSURE located inside FIRE
ENCLOSURS) shall comply with on of the following:
- be of FLAMMABILITY CLASS V-2 OR FLAMMABILITY CLASS HF-2; OR
- pass the flammability test described in clause A.2; or
- meet flammability requirements of a relevant IEC component standard which
includes such requirements.

Does this mean; if i have an enclosure inside a FIRE ENCLOSURE, than it has
to be V-2 eventhough there are no safety hazards resulting from complete
disapperance of the enclosure?

[Simple answer is "yes".  There are exeptions listed immediately following
the text you included above, e.g. parts mounted on materials of flammability
class V-1.]

thank you.

vijay wani









-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to