To be pedantic, you are mixing units of two different quantities there
Mike. Tesla and gauss are units of magnetic flux density, the B field
Ampere/metre and oersted are units of magnetic field strength, the H field.
Only in a vacuum does 1A/m generate a flux density of exactly 0.4 pi µT
In air its pretty close but in ferromagnetic materials it can be thousands
of times bigger. The field strengths mentioned in the original question
are not all that outrageous. Most transformers, motors and generators
with electrical steel laminations operate at peak flux densities of 1.4T to
1.7T
within the core. At a boundary  between two materials of different
permeabilities the tangential component of H and the normal
component of B are the same either side of the boundary.  The amplitude
relative
permeability of electrical steels near their maximum working flux density
is only about 300 to 800. So with the flux flowing along the core at a flux
density
of say 1.5T  and an amplitude relative permeability of 500, you
get a flux density close to the core surface of 3mT. While you are in the
near field
(distances small with respect to the size of the magnetic circuit) this will
not
drop very fast. in the far field it drops according to the inverse cube
dipole
law. Things are even worse at the corners. The flux does not turn smart
right
angles just because the core does and so the flux is not parallel to the
core. This increases the flux density close outside the core. Worse yet are
the
effects of  gaps. Laminations in transformers are commonly made in two parts
that fit together to form  the complete lamination. C & T shape or E and I
shape.
This is done so that the winding can be put on the  bobbin first and then
the core
built up. Where the two parts of the lamination meet up there is always a
small gap
the size of which depends on the quality of the laminations and the care
with which
the core is assembled. Good practice is to alternate the orientation of the
laminations so that the gaps do not align but in some cheap devices the
laminations are stacked up with the gaps aligned.These devices also tend to
be those using poorly cut laminations. Gaps of half a millimetre are not
unknown.they also tend to push the flux density  up closer to the limit
increasing the external flux
even more because of the lower amplitude relative permeability  Gaps in
rotating
machines can be even bigger .
Since the flux crosses the gap almost normally the flux in the gap is the
same as
 in the core 1.4T -1.7T At the edge of the core this flux bulges out into a
fringing
 field. Fortunately this enters the far field dipole law at distances large
compared
 to the gap length and width. Even so fields of tens of mT can be found
within a few
centimetres of the gap. So take a large poorly  built transformer or
solenoid and push
 the core hard up against the equipment housing and you could well exceed
0.7 mT nearby. Several metres from  a train is a bit less likely but not
impossible
These figures should be borne in mind the  next time
you read about the dangers of the magnetic field from overhead power
lines. I have several times seen building site welders sitting on their
transformers
with their testicles dangling over the gap and I haven't seen welders
dropping like
flies.

Nick Rouse



----- Original Message ----- ,
From: "Mike Cantwell" <[email protected]>
To: "emc-pstc (E-mail)" <[email protected]>
Sent: Friday, February 08, 2002 2:53 PM
Subject: RE: Teslars???


>
>
> I think the units you're looking to compare to would be Amps/meter. The
> conversion from Tesla to A/m is:
>
> 1 A/m = 1.26 uT = 0.0126 Gauss
>
> Therefore, a field of .7 mT converts to 555 A/m !!! (it is also equivalent
> to 10 Gauss)
>
> Assuming that your customer is referring to power frequency magnetic
fields,
> this would be substantial, to say the least.
>
> I would recommend that you question your customer a little further as to
how
> they determined this field strength requirement. It seems high by a factor
> of about 1000.
>
> Good luck,
> Mike
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]
> Sent: Thursday, February 07, 2002 4:22 PM
> To: [email protected]
> Subject: Teslars???
>
>
>
> We have a customer that is concerned about how our product, laboratory
> equipment, will respond to electromagnetic disturbances from a high speed
> train that runs close to their lab.  The customer states that the
> disturbance will be around 0.7-1.2 m Teslar.
>
> Can someone please explain what the unit Teslar is and how that unit
> relates, or if it relates, to the immunity tests of EN 61000-4-3 Radiated
> immunity, or any other immunity test.
>
> Has anyone ever had a similar concern from a customer dealing with this
> type of disturbance?
>
> Your responses are appreciated.
>
> Regards
>
> Joe Martin
> EMC/Product Safety Engineer
> Applied Biosystems
> [email protected]
>
>
>


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to