One key reason the US (and others) computer industry objects to IEC
61000-3-2 is that it was jammed down our throats with little or no input
from anyone other than the power providers.  They conveniently set the
limits so that the full cost of resolving the problem would fall on
producers (and consumers) of devices utilizing the power they provide.  No
standards were made that would require better design of the power
distribution system or consideration of facility level mitigation measures.
 
Fixing the power supply of a personal computer to meet the requirements in
IEC 61000-3-2 is simple - spend money.  The choke needed represents about a
10% cost adder to the power supply.  This is simply a cost, like taxes on
businesses, that is passed on to the consumer of the product.  Fixing the
problem costs money, but typically large equipment to fix a problem over a
larger area is more economical than fixing it one load at a time.
 
Let us agree to disagree.  I remain an opponent of IEC 61000-3-2 as written
and hope that TC77/SC77A does a better job with the version they are working
on and that it better represents a compromise between those who would put
the entire burden on the loads (as they have already done) and those who
would do nothing.
 
Ghery Pettit, NCE
 
-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Wednesday, January 23, 2002 2:27 AM
To: [email protected]
Cc: [email protected]
Subject: Re: EN 61000-3-3 compliant heater controller


Dear Ghery 
I am well aware of the undersized neutral problem, but given that we have a
legacy of buildings with undersized neutrals it is not a simple or low-cost
solution to uprate all their neutrals. 

Anyway, harmonics in the mains distribution cause many more problems than
simply overheating neutrals – waveform distortion is a greater worry. 

Since your negative approach to the need for harmonics control was similar
to views expressed in an article in Conformity Update 08-06-00, I originally
quoted from Mr van den Bergh's reply to that article. 

Mathieu van den Bergh is not just any ordinary old consultant, he is a
member of the TC77/SC77A Working Group that is responsible for IEC 61000-3-2
and appears to have a great deal of experience and knowledge in the area of
harmonics. 

He is also based in the US, where most of the 'denial' of harmonics problems
seems to arise, despite well-known problems with harmonics in the USA. 

I would have assumed that since you are knowledgeable in the field of
harmonics you would already know Mr Van den Bergh and would already have
discussed your concerns with him and (hopefully) come to some kind of
agreement. 

Since he appears to be an expert in these matters, I hope you will not mind
me quoting a little more from his August 19 2000 reply to Conformity Update:


"A number of studies in countries including Switzerland, the UK, France,
Scandinavian countries, Japan, and the USA, have shown that harmonic
distortion has increased from about 2 - 2.5% in the late 70's - early 80's
to about 4 - 4.5% in the mid-late 90's with distortion in heavily
industrialised areas reaching 6 - 7%!! 
It has also been proven through many studies and observations that harmonics
related problems increase significantly when distortion levels exceed 5% and
that they become very serious and costly when distortion approaches 10%. It
has been generally accepted therefore that distortion is increasing at 0.1 -
0.15% per year in industrialized nations. 
If no action is taken it is to be expected that distortion levels will start
to exceed critical levels within a few years." 

Notice Mr van den Bergh is referring here to waveform distortion, not
neutral currents or zero-phase flux in transformers, both of which are
problems only for individual sites not the distribution network as a whole.
He goes on... 

"The proliferation of electronic equipment with switch mode supplies falls
in the same category as the lighting related problems about 20 years ago." 

I agree with you that the harmonics problem can be ameliorated by actions
taken at the power distribution network level, or by actions at the load
level, but I have not investigated their relative economic cases. 

But whichever method is adopted, the customer pays the bill eventually and I
have more confidence in the highly competitive world of electronic products
to come up with a cost-effective solution in a timely manner. 

I have some knowledge of power-factor correction techniques in switch-mode
supplies, and some of them can cost very little indeed. So I really don't
know why the US computer industry is making such a fuss about controlling
harmonic emissions. 

It reminds me of the fuss the auto industry made about compulsory seat
belts, catalytic converters, etc., or the fuss the VDU monitor industry made
about meeting MPR2 – all those things that were stridently opposed by
manufacturers as needless added expense, or even impossible – yet we now
find them in all the products we buy even though they still cost less in
real terms than they did before. 

I suspect the real reason for the computer industry's denial of harmonics
problems, or else blaming them on a poor distribution system, is that US
computer manufacturers simply want to make one model they can sell
world-wide – so they want whatever is permitted in their main market (the
US) to be permitted everywhere else. 
Would you agree with this? 

Regards, Keith Armstrong 

In a message dated 22/01/02 17:34:47 GMT Standard Time,
[email protected] writes: 



Subj:RE: EN 61000-3-3 compliant heater controller 
List-Post: [email protected]
Date:22/01/02 17:34:47 GMT Standard Time 
From:    [email protected] (Pettit, Ghery) 
Sender:    [email protected] 
Reply-to: [email protected] <mailto:[email protected]>  (Pettit,
Ghery) 
To:    [email protected] ('[email protected]'), [email protected]
(Pettit, Ghery) 
CC:    [email protected] 

Keith, 

Many times the neutral cable problems result from using a smaller gauge wire
for the neutral in the mistaken assumption that the neutral doesn't carry
any significant current (true if the 3 phase load is balanced - when did you
last see that?).  Harmonics may make that problem worse, but the fundamental
frequency current can be a problem, as well.  The solution, used by many
building designers, is to use the same size wire for the neutral as for the
phase conductors. 

Do you expect me to believe that personal computers cause significant
harmonics problems?  There is no evidence of this in the U.S.  If there is
in Europe, then you are admitting that your power distribution system design
is deficient.  Lousy design on the part of the power providers is fixed by
saddling the manufacturers of the load with the full expense of the
solution?  Sorry.  I don't buy that approach.  A facilities solution is
usually more economical than fixing the 'problem' at each individual load. 

Quoting a few consultants is nice, but doesn't prove a case.  I remain a
total skeptic on this matter.  IEC 61000-3-2 needs (and is getting) a
complete overhaul.  IEC 61000-3-3 should be withdrawn.  Flicker is real, no
doubt, but this issue gets more attention than it deserves in the home
environment. 

Ghery Pettit 

-----Original Message----- 
From: [email protected] [mailto:[email protected]] 
Sent: Tuesday, January 22, 2002 2:23 AM 
To: [email protected] 
Cc: [email protected] 
Subject: Re: EN 61000-3-3 compliant heater controller 


Dear Ghery 
There is plenty of evidence, for harmonic problems, especially in large
cities and large office buildings. 

For example, an electricity supply engineer told me that in the financial
district in London there are buildings where they cannot fit any power
factor correction capacitors to the fluorescent luminaires - because they
fail within days due to the waveform distortion caused by harmonic currents.

So they have buildings drawing 100's of kA of lighting current at a low
power factor (< 0.6 I understand). I also understand they have overheating
problems with cables under the Thames connecting the two halves of London,
due to harmonic currents. 

In the early 90's I spoke with a USA-based consultant who told me about a
number of problems (e.g. completely burnt-out neutral cables) he had seen in
buildings in the US where they had installed lots of single-phase equipment.


'Banana Skin' No. 102 in the EMC + Compliance journal, Oct 2000 (read it in
the archives at www.compliance-club.com) describes harmonic overheating
problems with low-voltage lighting installations in hotels and public
buildings that has Fane Murray, a lighting consultant in the UK, very
concerned indeed. 

I understand that the power distribution in the USA is generally less
susceptible to waveform distortion than in Europe, nevertheless I understand
that the US has its own harmonics problems – Mathieu van den Bergh, of
Computer and Networking Services Inc., California said in August 2000: 

a)  for many years the US has had IEEE-Std-519 which has recommendations for
harmonic limits which are not much different from IEC 61000-3-2; 

b) the US lighting industry has voluntarily implemented ANSI harmonics
standards for fluorescent lamp ballasts that are more stringent than IEC
61000-3-2, as the direct result of serious harmonics problems in large
office buildings; 

c) the US Government has issued several large scale procurement requisitions
for Information Technology  that included far more stringent harmonics
requirements than those in IEC 61000-3-2. 

Time does not permit me to go through my files to provide a longer list of
real-life problems with harmonics. 

Regards, Keith Armstrong 
R>In a message dated 21/01/02 23:54:36 GMT Standard Time,
[email protected] writes: 



Subj:RE: EN 61000-3-3 compliant heater controller 
List-Post: [email protected]
Date:21/01/02 23:54:36 GMT Standard Time 
From:    [email protected] (Pettit, Ghery) 
Sender:    [email protected] 
Reply-to: [email protected] <mailto:[email protected]>  (Pettit,
Ghery) 
To:    [email protected] ('John Woodgate'), [email protected] 

So rather than educating the public on the cause of flicker, we get saddled 
with a useless design requirement.  Typical bureaucracy - don't fix the 
problem, make it LOOK like you're doing something, at someone else's 
expense.  Just like the harmonics standard - fix a problem that doesn't 
exist. 

Ghery Pettit 