Thanks to all who responded on this subject, but especially to Ing. Gremmen.
The point I missed was that the CDNs are more than simply injection and
isolation networks.  They also function as THE ONLY transmission line
termination resistances.

----------
>From: "Gert Gremmen" <[email protected]>
>To: "Ken Javor" <[email protected]>, "Jim Conrad" <[email protected]>,
"john woodgate" <[email protected]>, <[email protected]>
>Subject: RE: common mode immunity coupling units
>Date: Fri, Nov 8, 2002, 5:35 AM
>

> Hi Jim,
>
>
> If you take a look at the setup, you would
> see that the EUT is not grounded, and any current flowing through the
> EUT will end (by means of other cables) on another CDN  having a fixed
> impedance of 150 ohm to the ground plane. The cables running from
> CDN-EUT-CDN
> are at 3 cm height, and will approximate a 150 ohm transmission line giving
> no rise to standing waves. The termination is not the EUT, but the other
> CDN.
>
> If the CDN is that large that any capacitive current to ground flows, then
> that
> would influence the result, and that is a part of the reasons that the CDN
> are limited to 80 MHz for reliable test set ups.
>
> If cables are unshielded the EUT cable-to-cable impedance would be in series
> with the transmission line affecting the results.
> If the EUT has one cable only this is the same.
>
> But non of these are contradictory with what happens real life immunity
> problem situations.
>
> The only thing worth to discuss is the value of the CM impedance
> of 150 ohm, and this value has been selected
> as an (arbitrary)  average of many measured CM
> cabling impedances as encountered in real life.
>
> One can discuss eternally about the value, but it is a
> compromise between 50 Ohm (too low) and infinite, which is too high.
> It is a value that can be realized over the defined frequency range
> and is feasible in terms of set up ( 3cm above ground).
>
> The ground plane is required for the return current and is metallic
> for reproducibility reasons.
>
> A 80 cm set-up is equally non representative for real life situations
> with the addition that the CM cable impedance is even higher
> and more difficult to inject current on, and that parasitic
> elements have a bigger impact on the results.
> Due to the increased distance , the environment of the setup must
> be much more tightly controlled and we would end up testing conducted
> immunity
> in a anechoic room or free space. Remember the conducted emissions (LISN)
> test
> set up which give most rise to discussion due to it's 40/80 cm set up.
> This is the also a reason  (among others) why the radiated immunity 80 cm
> set up
> lacks reproducibility.
>
> EN 61000-4-6 limits cabling length to 30 cm which is large for the highest
> frequencies in the test range (80-230 Mhz). Shortening will
> get better results.
> The new version of EN 61000-4-6 will also prescribe 30 cm leads for
> large EUTs by extending the ground plane vertically until 30 mm requirement
> can be met. It also contributes to better reproducibility
> by prescribing the application of maximum 2 CDN's at a (test) time,
> reducing the load of multiple CDN in parallel (on mult. cables) and
> bringing the load back to the desired 150 ohms.
>
> Basically, within it's limitations, this standard is easy to
> use, with limited investments and creates good reproducibility
> on small and medium sized EUT as long as CDN's are
> applied. Remember that this test allows for fast testing on PCB-level
> thus immunize equipment on PCB scale , preventing lots of
> problems on apparatus level.
>
> Work is going on to allow for CDN's to use in conducted emission
> tests instead of a LISN as immunity and emission are reciproke,
> and so should the test set up.
> The symmetry/asymmetry issue with LISN's needs to be resolved,
> but as emssion problems are mainly asymmetric (Common Mode) nowadays
> ( using a capacitor any symmetric noise can be suppressed)
>
> I have 3 years of experience with ten's of EUTs using EN 61000-4-6
> and have found the results satisfactory.
>
> Regards,
>
> Gert Gremmen
> Manager
>
>
> Ce-test, Qualified Testing
> ce marking and more ..
> EMCD  LVD  R&TTED  MDD  MD
> www.cetest.nl
> Electrical / Electronic Equipment
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]On Behalf Of Ken Javor
> Sent: Thursday, November 07, 2002 10:12 PM
> To: Jim Conrad; john woodgate; [email protected]
> Subject: Re: common mode immunity coupling units
>
>
>
> I must be missing something.  The controlled impedance concept would work
> for me if the cable-under-test (CUT) were a single-wire-above-ground (swag)
> transmission line terminated at either end in its characteristic impedance.
> That is never the case.  If a cable is shielded, then it is terminated at
> the equipment-under-test (EUT) in a  low impedance and if it is not shielded
> its termination impedance reflects whatever circuit it is connected to, and
> whether that circuit is referenced to ground.  Actually that statement about
> a shielded cable being terminated in a low impedance reflects my vehicle
> experience.  Equipment designed for home or business use may well terminate
> a shield at an equipment chassis, but that chassis may or may not have a
> connection to ground, and even if it does it is a green wire of
> indeterminate, but not low impedance over the frequency range of the test
> (0.15 - 80 MHz).  And ditto for an unshielded wire - the circuit to which it
> connects may be referenced to chassis but chassis is not well-referenced to
> the ground plane - in fact I do believe that CDNs built for power ports
> inject on phase, neutral, AND green wires simultaneously - clearly implying
> that the green wire is just one more fortuitous conductor.
>
> If you are using a CDN or the injection clamp (the device that looks like an
> absorbing clamp but is used to inject) then the device does raise the
> impedance of the CUT looking toward the auxiliary equipment (AE).  But that
> alone is hardly enough to prevent standing waves.  The test technique does
> provide that injection should occur within a tenth wavelength at the highest
> test frequency, which should be sufficient to ensure that you know what
> level of signal gets into the EUT, provided the cable is unshielded.  If the
> cable is shielded, what gets into the EUT is not strongly a function of the
> exact position of the injection device relative to the EUT, but where
> standing waves may be relative to shield discontinuities, such as shield
> terminations.
>
> In conclusion, while I don't have a problem per se with IEC-10004-6, I don't
> know why they went to the trouble of requiring the "vehicle-like" ground
> plane set up when the same set up as 1000-4-3 should have sufficed.
>
> But like I said at the beginning, maybe I'm missing something.
>
> ----------
>>From: "Jim Conrad" <[email protected]>
>>To: "Ken Javor" <[email protected]>, "John Woodgate"
> <[email protected]>, <[email protected]>
>>Subject: RE: common mode immunity coupling units
>>Date: Thu, Nov 7, 2002, 6:37 AM
>>
>
>> Ken,
>>
>> The test set up is over a ground plane with controlled impedances to
>> make the test more reproducible.  It is not perfect but it's better
>> than having the EUT 80 cm above the ground plane where the
>> impedances would be very high and harder to control.
>>
>> Best regards,
>>
>> Jim
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]]On Behalf Of Ken Javor
>> Sent: Wednesday, November 06, 2002 10:54 PM
>> To: John Woodgate; [email protected]
>> Subject: Re: common mode immunity coupling units
>>
>>
>> I have to agree with Mr. Woodgate's comment, as far as numbers go -
>> 150 Ohms
>> means the wire is very close to a well-defined ground plane if the
>> number
>> represents a transmission line characteristic impedance.  However,
>> the IEC
>> 1000-4-6 test set up does not represent the real world, because it
>> requires
>> a well-defined low impedance ground plane underneath the entire test
>> set-up.
>> In my opinion, the set-up ought to look precisely like the IEC
>> 1000-4-3 set
>> up (80 cm above ground), since the purpose of 1000-4-6 is to
>> simulate the
>> results of radiated field-to-wire coupling at frequencies too low to
>> accurately simulate in a practical radiated set-up.
>>
>> I am curious to hear what Mr. Woodgate and others think about this
>> topic.
>>
>> ----------
>>>From: John Woodgate <[email protected]>
>>>To: [email protected]
>>>Subject: Re: common mode immunity coupling units
>>>Date: Tue, Nov 5, 2002, 3:08 PM
>>>
>>
>>>
>>> I read in !emc-pstc that Ken Javor <[email protected]>
>> wrote
>>> (in <[email protected]>) about 'common mode
>> immunity
>>> coupling units' on Tue, 5 Nov 2002:
>>>>Because the Europeans think that is the right impedance to
>> simulate a
>>>>generic transmission line/antenna far from ground.
>>>
>>> Not 'far' from ground, AIUI, but 'not far' from ground.
>>> --
>>> Regards, John Woodgate, OOO - Own Opinions Only.
>> http://www.jmwa.demon.co.uk
>>> Interested in professional sound reinforcement and distribution?
>> Then go to
>>> http://www.isce.org.uk
>>> PLEASE do NOT copy news posts to me by E-MAIL!
>>>
>>> -------------------------------------------
>>> This message is from the IEEE EMC Society Product Safety
>>> Technical Committee emc-pstc discussion list.
>>>
>>> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>>>
>>> To cancel your subscription, send mail to:
>>>      [email protected]
>>> with the single line:
>>>      unsubscribe emc-pstc
>>>
>>> For help, send mail to the list administrators:
>>>      Ron Pickard:              [email protected]
>>>      Dave Heald:               [email protected]
>>>
>>> For policy questions, send mail to:
>>>      Richard Nute:           [email protected]
>>>      Jim Bacher:             [email protected]
>>>
>>> All emc-pstc postings are archived and searchable on the web at:
>>>     http://ieeepstc.mindcruiser.com/
>>>     Click on "browse" and then "emc-pstc mailing list"
>>>
>>
>> -------------------------------------------
>> This message is from the IEEE EMC Society Product Safety
>> Technical Committee emc-pstc discussion list.
>>
>> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>>
>> To cancel your subscription, send mail to:
>>      [email protected]
>> with the single line:
>>      unsubscribe emc-pstc
>>
>> For help, send mail to the list administrators:
>>      Ron Pickard:              [email protected]
>>      Dave Heald:               [email protected]
>>
>> For policy questions, send mail to:
>>      Richard Nute:           [email protected]
>>      Jim Bacher:             [email protected]
>>
>> All emc-pstc postings are archived and searchable on the web at:
>>     http://ieeepstc.mindcruiser.com/
>>     Click on "browse" and then "emc-pstc mailing list"
>>
>
> -------------------------------------------
> This message is from the IEEE EMC Society Product Safety
> Technical Committee emc-pstc discussion list.
>
> Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
>
> To cancel your subscription, send mail to:
>      [email protected]
> with the single line:
>      unsubscribe emc-pstc
>
> For help, send mail to the list administrators:
>      Ron Pickard:              [email protected]
>      Dave Heald:               [email protected]
>
> For policy questions, send mail to:
>      Richard Nute:           [email protected]
>      Jim Bacher:             [email protected]
>
> All emc-pstc postings are archived and searchable on the web at:
>     http://ieeepstc.mindcruiser.com/
>     Click on "browse" and then "emc-pstc mailing list"
>
> 

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

All emc-pstc postings are archived and searchable on the web at: