Jim
 
I your case the required BASIC INSULATION is not present or adequate. BASIC
INSULATION provides a level of protection. The branch circuit provides an
additional level of protection if there is a failure of the BASIC INSULATION.
The standard in this instance allows the designer to provide an alternate
protection method to replace the BASIC INSULATION, with the requirement that
it fails safe and it does not impact any other insulation system. 
 
Regards,
Kurt Mikolajewski


From: Jim Eichner [mailto:[email protected]]
Sent: Tuesday, January 28, 2003 5:13 PM
To: [email protected]
Subject: RE: Circuit Breaker Tripping Dring Fault Tests


I've been trying to solve this one myself.  I work with one pair of standards
(UL458 / CSA107.1) where they specifically say that opening the branch circuit
protection is acceptable during component fault testing, but NOT during short
circuit tests done for the purposes of validating inadequate trace spacings
(an easement offered in the standards in some situations).  I've always been
puzzled why we can't rely on branch circuit protection for both situations,
but neither agency has been able to explain the difference to me.
 
Jim Eichner, P.Eng.
Regulatory Compliance Manager
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: [email protected]
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 




  _____  

Do you Yahoo!?
Yahoo!  <http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com> Mail
Plus - Powerful. Affordable. Sign up  <
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com> now


Reply via email to