As a fuse manufacturer, I have read all the e-mail on this subject with great
interest.  Unfortunately, many responses emphasize common misunderstandings.

In the fuse industry, there is no such thing as a "Bad" fuse.  The chain of
e-mails clearly indicate why we avoid this word due to its various meanings. 
Similarly, we try to avoid the word 'failure'.  A "bad" or 'failed' fuse can
mean any number of things, but the most common is that the fuse is open, (it
operated).  Thus, the fuse did what it was supposed to do - operate - and yet
it is deemed 'bad' or a 'failure'.

There are numerous occasions when a customer returns a 'bad' fuse.  The fuse
was 'bad' because it operated properly.  In many instances, the choice of fuse
type or amperage rating was flawed.

For being such a 'simple' device, there are many items that influence the
correct choice.  I will address some of these by picking quotes out of the
various e-mail on the subject.  Among these are:

*       Voltage rating - (This was addressed in Mr. Richmond's e-mail - I've 
heard
of a "bad" fuse, in this case, a fuse not adequate to protect the circuit and
user.  A 30 volt fuse can't be counted on to interrupt a 408 volt circuit. 
This is absolutely correct.  Choosing a voltage rating below your application
can be very dangerous. 

*       Continuous Current rating  - This was addressed in Mr. Beckwith's 
e-mail -
Fuse operation when there is no fault can also sometimes be caused by
incorrect specification at the design stage, i.e. the fuse is rated too low
for the actual current consumed.  Very true.  One must look at surges
mentioned below and temperature.

*       Temporary Surges that you want the fuse to pass - A time delay fuse is
typically chosen for motor or transformer applications.  This is addressed a
little in Mr. Beckwith's e-mail - We have all seen cases where a fuse blows
when there is no apparent fault in the equipment, hence the maintainer's
comment "bad fuse". In my experience, this is usually caused by a temporary
overload condition or a power surge, not a "bad" fuse.

*       Temporary Surges that you do not want the fuse to pass.

*       Ambient temperature rating - This was addressed in Mr. Hughes e-mail 
below. 

*       Interrupting Rating - This was addressed in Mr. Hughes e-mail - A 
couple of
other common design drop-offs I would like to mention include failure to
select a fuse with an adequate prospective fault current (i.e. selecting a
5x20 mm glass fuse - rated at Isc=35A max and using it in a mains circuit
where the prospective fault is in the order of 1kA) and 'forgetting' to
de-rate the fuse for use in a high ambient temperature (although this has
already be mentioned re. pico-fuses).  

*       Shock/Vibration - Most fuses do not claim to be suitable for such
applications.  From Mr. Schlentz - I have seen one instance where a fuse
opened during a vibration test.  I think that was a BAD FUSE.  I don't know if
the fuse in question was supposed to be suitable or not.

  

If chosen incorrectly, and 'nuisance' opening occurs, as Mr. Powell mentions -
Often the answer is, increase the fuse size to prevent nuisance trips.  The
risk, of course, is that for every incremental increase in fuse value, you
increase the risk of fire proportionally.  In doing this, you may be defeating
the purpose of having the protection there in the first place.  If a fuse
nuisance opens, it is likely that one of the above bulleted items was
overlooked.

Additionally, as Mr. Richmond points out - Many fuses ARE mechanically
fragile; it's simple physics that says a low-current fuse will be a fragile
thread.  Think of them as light bulbs.  We do not call a light bulb unreliable
if it fails after being dropped on the floor; we call it broken.  This is
particularly true for low amperage fuses. 

As Mr. Beckwith points out - AIUI, there is a specified time it takes the fuse
to operate at 200% of the rated current, so for example a 1A normal blow fuse
requires 2A for approximately 10 seconds to go open circuit.  This time
reduces exponentially as the current increases.  There are different opening
time requirements depending on the type of fuse, (Time Delay versus Fast
Acting), and its physical size.  The 135%, 200% and/or 500% opening times are
documented in the tri-national, harmonized 248 Series of fuse Standards,
(248.1 through 248.16 - The standards are UL, CSA, and ANCE).   

If anyone has any specific questions, or would like more information, send me
a separate e-mail and I'll see what I can do.

Dan 

Manager, Industry Standards & Certifications 
Cooper Bussmann 




Reply via email to