The answer from EN50091-1-1 is... Worst case voltage within the range specified by the manufacturer. If a range is not specified, it's +6%, -10%. Note that this over-rules the '950 bit about increasing that range to +10% for 230Vac single-phase or 400Vac 3-phase. This version of the UPS standard uses the old EN60950 +A1 +A2 as a reference.
>From EN62040-1-1, the answer is slightly different. This version of the UPS standard uses the new EN60950-1 as a reference, and accepts its requirements of 1.4.1, 1.4.2, 1.4.3, 1.4.6, 1.4.7, 1.4.8, 1.4.10, 1.4.11, 1.4.12, 1.4.13, and 1.4.14 as is (but not the missing subclauses) and then adds a note saying only the heating and leakage tests are done with voltage tolerances, all the rest being done at nominal voltage. Hope this helps, Jim Eichner, P.Eng. Compliance Engineering Manager Xantrex Technology Inc. e-mail: [email protected] web: www.xantrex.com Any opinions expressed are those of my invisible friend, who really exists. Honest. No really. Confidentiality Notice: This email message, including any attachments, is for the sole use of the intended recipient(s) and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies of the original message. From: Nick Williams [mailto:[email protected]] Sent: Thursday, July 03, 2003 1:29 PM To: [email protected] Subject: EN50091-1 question I have a need to know a detail of the above standard more quickly than I can obtain a copy, if someone would be so good as to help me. What is the voltage range (percentage of rated voltage) defined for heating and other tests in the above standard for normal and abnormal operation? Any help in this regard appreciated. Nick. This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: [email protected] with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: [email protected] Dave Heald: [email protected] For policy questions, send mail to: Richard Nute: [email protected] Jim Bacher: [email protected] Archive is being moved, we will announce when it is back on-line. All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: [email protected] with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: [email protected] Dave Heald: [email protected] For policy questions, send mail to: Richard Nute: [email protected] Jim Bacher: [email protected] Archive is being moved, we will announce when it is back on-line. All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc