>from IEC site: 

IEC 61000-3-4 
Limits - Limitation of emission of harmonic currents in low-voltage power
supply systems for equipment with rated current greater than 16 A 

  
Abstract: The recommendations of this technical report are applicable to
electrical and electronic equipment with a rated input current exceeding 16 A
per phase and intended to be connected to public low-voltage a.c. distribution
systems of the following types:

- nominal voltage up to 240 V, single-phase, two or three wires; 
- nominal voltage up to 600 V, three-phase, three or four wires; 
- nominal frequency 50 Hz or 60 Hz. 
These recommendations specify the information required to enable a supply
authority to assess equipment regarding harmonic disturbance and to decide
wether or not the equipment is acceptable for connection with regard to the
harmonic distortion aspect.

luck, 
Brian 

-----Original Message----- 
From: POWELL, DOUG [ mailto:[email protected]] 
Sent: Monday, August 11, 2003 8:50 AM 
To: EMC-PSTC (E-mail) 
Subject: Power line current injection 

Hello group, 

Is there anyone that can tell me the current status of the limits power
harmonics for products over 16A per phase?  I am interested in both Europe and
North America.

Also, I have heard that Japan has gone ahead of Europe with this and that the
limits are similar to the European draft.  Is this true?

Thank you, 
-doug 


Reply via email to